djelectric
I am hoping someone could give me some reassurance here..
I am fitting a towel radiator in my bathroom. I want to use both the central heating and a heating element to heat the rad.
I don't want the element to be active whilst the central heating is running.
I have carried out some tests on my Danfoss TP9000 thermostat/programmer and there is an available terminal named 'OFF HTG' that when testing with a voltage indicator against a neutral it becomes live when the thermostat is not calling for heat, and becomes dead when it is calling for heat..
This would be perfect for connecting up my element! I have checked the specs of the TP9000 and all terminals are switch current rated at 3A, the element demands 1.7A (400w @ 230v) so I believe the unit is sufficient to drive it (please inform me if I'm wrong here).
The main thing I am concerned about is protecting the element and its provided cable with the 5A fuse recommended by the manufacturer.. Would it be ok to connect in the following sequence:
32A RCBO feeding kitchen ring in CU > 13A SFCU (feeding boiler and controls) > TP9000 > 13A FCU (in zone 2 of bathroom adjacent to rad) > element.
The boiler SFCU has a 13A fuse protecting 2.5mm2 T+E feeding heating systems.. FCU for element will have 5A fuse as stated above..
Anything wrong here?
Hmm. The boiler SFCU should contain a 3A fuse unless there's a good reason to choose otherwise. It's not just protecting the bit of 2.5mm² cable, it's protecting the boiler and its controls.
The electric heating element is thermostatically controlled so if the heating were on and had heated the towel radiator above the element set point the element would be off anyway.
Even if the heating temperature was below the element temperature the element would be n for a very short time as it heated the rail a couple more degrees.
Usually the electric element in a 'dual fuel' towelrail is connected via an appropriately fused FCU on a permanent supply, the electrical part is generally switched on as required during the months when the main heating system isn't needed. With your method the element would be powered at all times when heating was off on the programmer/stat unless the main isolator was off. Therefore it would generally be running right through the night which could be quite costly.
The electric heating element is thermostatically controlled...
Really? I thought that they were usually sized to warm up the radiator to a reasonable surface temperature and be effectively self-limiting due to their low power.
I've never knowingly fitted one with an integral thermostat.
Thanks for your replies!
I missed a little info out.. I plan to use a timer between the fused spur and the TP9000 to set appropriate times for the rail to be heated, i.e. switched off completely at night then back on early morning to warm the towels.
Also gave Tesla UK (element manufacturer) a call earlier today with queries about the element as the instruction manual states 'DO NOT TURN THE ELEMENT ON WHEN THE CENTRAL HEATING IS ON'. The technician informed me it was completely safe to do this, but will be uneconomical as the element will be heating the already heated central heating water.. The built in thermostat is programmed to trip at 75 degrees C, which the central heating wont trigger as it only reaches around 60 degrees..
It is a 'permanently on' element unless controlled by an external timer/thermostat.
I just feel the method I've stated will give the best control..
Will also look into fitting correct fuse for boiler SFCU.. I only noticed it today.. Council fitted stuff you know what its like! Had a periodic inspection done early this year and it went through..
The flaw in your control is when the room temp is up and the stat clicks the boiler off you then have the element coming on to heat a already hot rail (timer permitting).
Why not fit a pipe mounted stat' or thermocoupler and temp' monitor that will ensure that if the system has hot water circulating then it won't let the element switch on.
You could well be right, I am not really thinking perhaps.
Overall a time switch is easier than messing about.
Why no fit a pipe stat' that will ensure that if the system has hot water circulating then it won't let the element switch on.
That's a good point.. Could you point me in the direction of such stat please? This would be very helpful.
So would you deem the rest of the setup is acceptable then? Once I correct the fuse for the boiler.. I was worried about spurring off a spur essentially.. And switching the spur using the 9000 stat.. Cant see anything in the regs on this, just know its not the best of practices..
I would find out what rated fuse the boiler required, and what load it required, this would be the limiting factor to your original proposal having said that, its not a concern now as you can have a dedicated spur for your rail now and either spur it off the ring and bring in a radial, also your pipe stat' can be located out of sight say in an airing cupboard or anywhere convenient for the piping and a little joint box.
Right, so I forget tapping into the central heating thermostat altogether and use a dedicated spur, pipe stat and a timer to control it..
Seems easy enough.. And will save me even more energy (beer money).
Thanks mate, really appreciate the advice!
Don't forget we have a 'Thanks' button on the orange tab too .. it gets our thanks tally up :devilish:
I want the element to switch off whenever the central heating comes on. Regardless of the timers I've got set. Heating is on quite often in the winter, no point having the 400W element running at the same time.
Turn it off then...
Turn it off then...
? So every time I want the rad to warm up I have to think in advance and manually switch it on?
Or just have it do it automatically using the pipe stat and timer..
The stat will turn it off for me.. and the timer will warm it up before we all get up in the morning for showers/baths.
Why bother with the pipe stat? Just turn it on or off when required.
We could say the same with half the household gadgets, why bother with the remote control just go to the tele and turn it over.. we live in a lazy society and people like things they don't have to remember or manage.. convenience sells itself ;)
Maybe so, but why not.. Doesn't take much more effort and the stat is only a tenner.
as as long as it's not in some unsuspecting customers home then carry on.
me thinks the fcu timer unit is the best bet, just switch it off fro mid October to mid march when the heating should be on!
Darkwood, would it matter which leg I stick the stat on, flow or return? Both are available in a cupboard outside the bathroom which is the perfect spot for it.
No just put it on a timer FCU and set the timer for the periods you want it to turn on and off. Obviously the periods you wish to time will be set when your heating is turned off via the time clock/programmer.
Yea but as I said before, if someone decides to turn the central heating on manually (which we do all the time) and this overrides the timer, the element is still going to be on for no reason if its within the time its set to be on.
Cant see why an unsuspecting customer would have an issue with the setup, but this is for my own home anyway.
I know what your trying to say, but your missing the point, it will be a waste of electric having the element on at the same time as someone switching the heating on manually (outside the set time of the timer).
The thermostat will be set to a temp so that when the central heating comes on the element will not power up. A timer set at the opposite times of the central heating timer would work until someone manually switches the heating on.
Or I could just move to Barbados where the weather is hot all year round and be done with all this!
TBH it won't make too much difference as you have an adjustable stat and the temp' loss through the towel rail won't be that big but if you have to choose then the flow will give a more accurate temp of the water won't vary if a big wet towel is draped on the rail where the return is subject to variable heat loss dependent if you are actively using it to dry things.
Dual fuel towel radiator
Central Heating Systems
Thread Tags
djelectric,
Darkwood,