W

wisesparky

Hi guys.
Run a 10mm to out building for garage board, out building is connected to house and it is twin and earth, as the regs state needs to be rcd protected (less than 50mm etc) but the board i got has an rcd in it to?
So what im asking is there any implications to having 2 rcd's on 1 circuit.
Many thanks guys:)
 
Hey.

With two 30mA RCD's in line there would be no discrimination between the two so in the event of fault there is no way of telling which would trip first.

What I would say is that as you already have 30mA RCD protecting the sub-main then you dont really need another one in the DB at the garage end to protect the sockets and lights as you already have it at the house end.

How is your sub-main cable installed is it surface all the way??
Do you have any spare unprotected ways in your house DB??

You may (depending on various factors) not have to protect the sub-main with 30mA RCD and could have it on normal 32A MCB on unprotected side.

Cheers:D
 
Hey.

With two 30mA RCD's in line there would be no discrimination between the two so in the event of fault there is no way of telling which would trip first.

What I would say is that as you already have 30mA RCD protecting the sub-main then you dont really need another one in the DB at the garage end to protect the sockets and lights as you already have it at the house end.

How is your sub-main cable installed is it surface all the way??
Do you have any spare unprotected ways in your house DB??

You may (depending on various factors) not have to protect the sub-main with 30mA RCD and could have it on normal 32A MCB on unprotected side.

Cheers:D
Thanks for getting back to me.
The cable is run below floor boards and down a wall (about 20mm in) befor going out to were i will be putting new board.
was going to put it on 40amp breaker witch is covered by rcd.
so i should just get new board with a main switch and 6 and 16 or 32 amp breaker??
Once again thanks for your time.
 
Hey mate.

As the sub-main cable needs 30mA protection then a unit as you have described for the garage will be fine.

Just make sure your RCD disconnection times are within limits.

Cheers.:D
 

Reply to Dual rcd???? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
778
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
681
davesparks
D
  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
824

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top