B
beaver74
can any one give me rattings on duel heat setting showers you know the one that have 2 heat settings have got a 9.5KW that has been install on 6.00mm and the customer has gone by manial that said 6.00mm but it is running through a ceiling which i can not tell if it is insulated if lower heat setting is about 8kw /240v= 33.33A i will disconect additional element and leave it as 8.KW on the 32A breaker