I need to modify some machinery stop circuits but I don't want to do anything that would be detrimental to the standard requirements. Does anyone know where I can find the definitions of the Catagory 2, 3 etc that the standards quote. More specifically would it be allowed to daisy chain many NC E-stops to a bog standard relay and wire that to the Safety Relay as opposed to the contacts directly to it as at present? This would help me in building a monitoring systen for each E-stop without interfering with the operation of the Safety Relay. Thoughts welcome...
 
More specifically would it be allowed to daisy chain many NC E-stops to a bog standard relay and wire that to the Safety Relay as opposed to the contacts directly to it as at present?

No because a standard relay has the risk of failing to operate.

You say you want to add monitoring to the e-stops. Do you want to know which specific e-stop has been activated, or just a single alarm when any e-stop is hit?

Can you provide more details of the type of equipment and exactly what you want from this safety circuit?
 
To answer xraytek's question, yes I want to know which stop is activated. Take this specific example: I have a DOLD Safemaster relay with 8 NC guard switches series wired in the S11 -S12 monitored stop circuit. In the past an LED has been used as an indicator accross each switch contact to indicate which switch is open, however this is a little hit and miss (and probably not officially recommended) because on occasion the 10mA current through the LED is enough to upset the Safemaster. It is not that the unit does not drop out, but sometimes it will not reset properly. What is the normal approach to the problem of a visual indication of which guard is open?
 
I was waiting for that one silva.foxx! The switches are already 2 x NC as they signal to the main plc that controls the machine. Unfortunately I waste many hours tracing faults whereby the switch ( limit switches or key interlocks) is stuck between open & closed, giving an ok signal to the plc, but no circuit on the e-stop, or indeed the other way round! I need a way to monitor the ACTUAL e-stop contact. Hope this clarifies.
 
Are there many e-stops?
One option is wire each e-stop into its own local safety relay, then loop your DOLD Safemaster relay through each relay.
A spare set of contacts on each new relay could then be used for monitoring.
 
Yes there are many e-stops. To give you some idea I have manufacturing machines 23 m long that have 8 to 12 guard switches per relay, and up to 10 relays per machine. We have 15 machines. A more cost effective method is preferred!
 

Reply to E-stop safety circuits in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K
Plus one for walking away and not getting involved in the design changes. If however you want to know a bit more about safety circuits for your...
Replies
7
Views
1K
What performance level are you aiming for? It’s whole body access, so Pld or Ple? This is pretty much the first port of call before deciding on...
Replies
2
Views
1K
  • Sticky
Hi Richard, thanks for your comment. The relay is rated 12A peak. It's also worth noting that a relay contact will perform differently depending...
    • Like
    • Winner
Replies
4
Views
2K
SOLVED Thanks for all the help. It was nothing to do with the smoke detector. In this new hole (where there will be a light fitting) three white...
    • Like
Replies
24
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks