Working on a old property in a slightly remote area installing a new circuit.

When I looked at the earthing it looked like a tns but I investigated and found a old 2.5mm running towards the rod.

My problem is I am getting a ze reading of 0.25 ohms.

Ino we had a really heavy down poor the day before but to be that low?

I am wait for the dno to confirm the earthing but they ain't rushing.

Any thoughts
I know a good reading for tt is 200 ohms or lower. This is the first one I have worked on
 
Thats is just the main cable nothing else

When I manage to peak around the wooden board covering the mains it looked like a swa with a earth strap.
It's under the stairs and I could hardly fit my head in there.
 
If you have an earth connection to the sheath of the supply cable and the Ze reading with all other earthing connection disconnected is 0.25Ω then the supply is TNS.
If it has a rod connected to the MET then there is an earth rod connected to the MET it would not change the earthing of the supply.
 
As I said I assumed it was a swa.
But looking out side there was only 2 cables going in.
So I would say that was a tube of some sort

This place has had works done but no one has left any certificates

I will have to contact dno again to comfirm the earth.
 
Hi Alan - I've been building up my TT portfolio lately using the larger 5/8" 4ft rods, two at a time. Around here in wet clay this has been good for 10 Ohms or less. I would need to parallel up many many of these to get your numbers, so it's def a DNO means of earthing in my humble opinion. Have you checked Ze against short circuit impedance? Avoid the non trip setting, if you get 0.25 for both then perhaps DNO has PME'd an old TT at some point.
 
It's a area they just keep adding to
There is power pole then when you get to a built up area they stop.

Can't find a substation near by.

I don't know if this may affect it but there is a dyke around the place and it on a flood plane
Ground soft and soak water in
 
Properties can be fed from pole mounted transformers not necessarily near a substation.
There is a method of earthing very occasionally used on single properties in remote locations fed from their own transformer (pnb).
Have you looked at the pole(s) supplying? If a pme overhead supply there should be a pme label on every third or fourth pole plus you will see an earthing conductor running down the pole.
 
Hi Alan - I've been building up my TT portfolio lately using the larger 5/8" 4ft rods, two at a time.

Sorry OP for hijacking your thread. Wiko what surveying do you do, if any, when choosing a place to install your earth rods, so as not to hit any other services?

Just curious as I've not done one yet, and if the 18th has its way, I'd better get some practise in.
 
Properties can be fed from pole mounted transformers not necessarily near a substation.
There is a method of earthing very occasionally used on single properties in remote locations fed from their own transformer (pnb).
Have you looked at the pole(s) supplying? If a pme overhead supply there should be a pme label on every third or fourth pole plus you will see an earthing conductor running down the pole.

I have a three wire overhead supply from a pole transformer, bare and only the line (live lol) insulated from the last pole to the house. Three houses on this one supply.
 
Hi Alan - I've been building up my TT portfolio lately using the larger 5/8" 4ft rods, two at a time. Around here in wet clay this has been good for 10 Ohms or less. I would need to parallel up many many of these to get your numbers, so it's def a DNO means of earthing in my humble opinion. Have you checked Ze against short circuit impedance? Avoid the non trip setting, if you get 0.25 for both then perhaps DNO has PME'd an old TT at some point.

I found those rods give a much better reading myself, going to use them from now on.
 
I found those rods give a much better reading myself, going to use them from now on.

Same question for you Phil;

Sorry OP for hijacking your thread. Wiko what surveying do you do, if any, when choosing a place to install your earth rods, so as not to hit any other services?

Just curious as I've not done one yet, and if the 18th has its way, I'd better get some practise in.
 

Reply to Earth arrangements confusion in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
278
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
270
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
351

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
I think I might be tempted to test this theory, if it can be done without causing danger to anyone.
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top