I've seen the posts dealing with this, but none seem to state a solution I can comprehend I therefore submit the following scenario:
A three pin IEC lead connect to an adaptor that outputs to an 0.5m 18AWG four pin DC connector that plugs into a TV.
Transformer outputs 12V 4A and neither it nor the TV has any symbols.
IEC lead is tested as standard class 1 with an Earth Bond result of 0.05
IEC lead is attached to transformer block and Test Lead attached to pins inside DC connector and Earth Bond test returns 0.32
As there is a return do I assume that the Earth cable is continuous and fail it or do I treat it as low voltage and not test either the transformer or TV beyond visual inspection?