External oil boiler, (just outside kitchen) oil pipe buried through garden to tank. Plumber says it doesnt need bonding as its outside? Am i missing something?? Copper pipes entering house from boiler.
Thoughts
 
Hi - guessing the boiler will be earthed via cpc, but any pipe entering the house may need bonding I'd have thought. Perhaps confirm installation instructions whether the external boiler, external oil tank and pipework needs any special treatment. Maybe Mr Plumber's done that?
 
Last edited:
I agree if the pipes entering the property from the boiler are also copper then this is bringing an extraneous conductive part into the installation and requires a main equipotential bond.
I though that pipes had to be copper within 3 meters of a boiler but could be very wrong on that?!
 
The PME requirements are that the tank/pipework (external) is staked down. Internally, as always a bond is fixed on the consumer side of the tap and any insulated insert. This has nothing to do with wiring regulations which are non mandatory.
 

Reply to Earth bond to external oil boiler.... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
L
  • Article
Underground oil tank feed problem This unit is located in France where they use diesel not kerosene. The feed from the underground tank is not...
Replies
0
Views
184
LostinFrance
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top