TripleJay

first post so not sure if this is the right forum. I could do with a little bit of electrical advice.... It's to do with earthing straps in the kitchen. Replaced the sink taps... previously the pipes going up to sink had an earth strap each got and cold. Water pipes are plastic speedfit, apart from tails to tap which were copper and had earth straps fitted. Now just got plastic pipes connected to braided hoses for taps.... any advice appreciated... cheers...
 
The 'earth straps' were probably fitted some years ago, when your install did have copper pipes. It would do be pointless to attach them to the braided hoses for the taps.

The only other consideration is whether, below your sink is where your main water service enters your property, and perhaps should be bonded. If you have a plastic service, it does not require bonding. However the OSG recommends bonding metal pipes after plastic service, unless it can established that said metal pipes are not introducing a Earth potential.

The bonding of hot & cold services (previously under your sink) may have been the location where the original electrician chose to supplementary bond (which may or may not be still be required in your property). Are you an electrician?
 
The 'earth straps' were probably fitted some years ago, when your install did have copper pipes. It would do be pointless to attach them to the braided hoses for the taps.

The only other consideration is whether, below your sink is where your main water service enters your property, and perhaps should be bonded. If you have a plastic service, it does not require bonding. However the OSG recommends bonding metal pipes after plastic service, unless it can established that said metal pipes are not introducing a Earth potential.

The bonding of hot & cold services (previously under your sink) may have been the location where the original electrician chose to supplementary bond (which may or may not be still be required in your property). Are you an electrician?

Thanks. No, I'm not an electrician. The mains supply into the house is in another room.... not sure what to do with the two earth wires I now have loose under my sinks... thoughts?....
 
It is a bit of a dilemma. Is there one green or green/yellow single cable connected (i.e. the cable comes from somewhere else) to one of these two clamps and then to the other clamp, or is there just one such cable between the two?
 
I suspect they were irrelevant in the first place some electricians will connect earth wires across pipework even if not required.
 
It is a bit of a dilemma. Is there one green or green/yellow single cable connected (i.e. the cable comes from somewhere else) to one of these two clamps and then to the other clamp, or is there just one such cable between the two?

image.jpg
 
Should I just strap them to the braided hoses, if nothing else it will stop them flapping about?..... about to get my cooker which is to the right of the sink, replaced. It will have an electric oven... not sure if that is relevant, but it is in arms reach of the sink, as is the cooker main switch... thanks for any advice...
 
Its difficult to tell from here. I would recommend you have an electrician inspect this and your main bonding of your water service. It may be that they are redundant as Westward suggested, but I would have that verified, to be sure.
 
Its difficult to tell from here. I would recommend you have an electrician inspect this and your main bonding of your water service. It may be that they are redundant as Westward suggested, but I would have that verified, to be sure.
Thanks
 
It's never been a requirement to supplementary bond pipes under the sink that are not extraneous pipework.
If the cold water feed comes in under the sink and it's extraneous then your protective bonding for the water goes there and that's it.
 
It's never been a requirement to supplementary bond pipes under the sink that are not extraneous pipework.
If the cold water feed comes in under the sink and it's extraneous then your protective bonding for the water goes there and that's it.

It may be that this point was used to carry out supplementary bonding, as required by current & previous regs, if required. Unlikely point I agree, but something that needs verifying. As regards whether the water service needs bonding or not, something the OP should seek advice from an on site electrician.

PS you've never replied to the chat we were having on this subject, you could make it #54 :)
 
It may be that this point was used to carry out supplementary bonding, as required by current & previous regs, if required. Unlikely point I agree, but something that needs verifying. As regards whether the water service needs bonding or not, something the OP should seek advice from an on site electrician.

PS you've never replied to the chat we were having on this subject, you could make it #54 :)
I'll have a look.
We could get to 60
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earth bonding question
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
12

Thread Tags

Advert

Thread statistics

Created
TripleJay,
Last reply from
Ian1981,
Replies
12
Views
6,837

Advert

Back
Top