Hello all
just wanted to check earth bonding to a gas pipe
the con unit is in the flat the gas meter is the other side of the upstairs flat on an outside wall
about 18 meters from con unit is 10mm earth still ok?

also if a lighting circuit is run in steel conduit and it is using the earth for protection is this ok?
I was on the understanding each circuit should have its own cpc

The lighting circuit is in conduit but if I attach a cable and pull and the cable snaps I wont be able to expose the cable again cant cut in to the ceiling (Strucutal)customer dosent want trunking or false ceiling
do I just put a note on con unit warning only class 2 equipmeant to be used Nic sell them
problem is how do I do R1 connect phase to conduit it reads 165ohms way out
any ideas please
 
Last edited by a moderator:
10mm for the gas bond is fine.

Have you done a Zs measurement on the lighting circuit???

Sounds like the joints in the conduit are corroding and the continuity resistance is getting higher.

A new CPC may be needed if this is the case.
 
Hi Lenny confused on the zs do I measure the conduit as earth
example where do I put my earth clip it taking zs from ceiling rose sorry if it sounds dumb never had conduit issues before:)
 
Hi.

Yes IF the conduit is the earth there should be an earth lead bolted onto the back of the conduit box and terminated at the ceiling rose.

How is the conduit terminated at the DB??? is it a metalclad one???
 
dont think ther is one the cables come from the lighting circuit to con unit 3 live 3 net no earth
sockets have 3 lives 3 net and 1 earth going to a conduit box in the ceiling
would it be easy to pull cables through to re wire they seem to go in to ceilin g by about 2/3 inches
 
sounds as if you are effectively dealing with a lighting system with no cpc unless you can find and correct the reason for the high R2.

you might want to have a read of THIS if you are not already familiar with it.
 
If the Zs readings are Ok metal conduit can be used as the CPC, The NIC advise that a visual inspection of ever light point and switch drop to verify that the fittings and accessories have been correctly connected to the conduit system as Lenny mentions with fly leads.
 

Reply to Earth Bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
833
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
931

Similar threads

  • Question
4-5 hours for 150? no chance, this is 2024, 150 for 2 hours maybe, that said an hour seems pretty quick, not sure he did the job right
2
Replies
23
Views
2K
  • Question
Hi, How did you get on with the wiring?
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top