Hello all
just wanted to check earth bonding to a gas pipe
the con unit is in the flat the gas meter is the other side of the upstairs flat on an outside wall
about 18 meters from con unit is 10mm earth still ok?
also if a lighting circuit is run in steel conduit and it is using the earth for protection is this ok?
I was on the understanding each circuit should have its own cpc
The lighting circuit is in conduit but if I attach a cable and pull and the cable snaps I wont be able to expose the cable again cant cut in to the ceiling (Strucutal)customer dosent want trunking or false ceiling
do I just put a note on con unit warning only class 2 equipmeant to be used Nic sell them
problem is how do I do R1 connect phase to conduit it reads 165ohms way out
any ideas please
just wanted to check earth bonding to a gas pipe
the con unit is in the flat the gas meter is the other side of the upstairs flat on an outside wall
about 18 meters from con unit is 10mm earth still ok?
also if a lighting circuit is run in steel conduit and it is using the earth for protection is this ok?
I was on the understanding each circuit should have its own cpc
The lighting circuit is in conduit but if I attach a cable and pull and the cable snaps I wont be able to expose the cable again cant cut in to the ceiling (Strucutal)customer dosent want trunking or false ceiling
do I just put a note on con unit warning only class 2 equipmeant to be used Nic sell them
problem is how do I do R1 connect phase to conduit it reads 165ohms way out
any ideas please