earth bonding | on ElectriciansForums
Discuss earth bonding in the Australia area at ElectriciansForums.net
M
Marc.Crroll
think i know the answer but just to confirm new regs state 10mm bonding from gas meter and water but is there a maximum distance before size needs to be increased
Every earthing conductor shall comply with section 543
The earthing conductor shall be calculated 543.1.3 or selected 543.1.4
If the adiabatic equation is used,the fault current is determined by the Zs
The Zs is partly determined by the cable resistance
The resistance is partly determined by the length
So if it is calculated then the size is chosen by the result ( where length of cable has been taken into account)
If it is selected then its done for you
Reply to earth bonding in the Australia area at ElectriciansForums.net
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...