can some one help me as confused

a few people have said diffrent things about this

i am about to rewire a theatre building and it has 2 boilers, now do i need to have a main earth bond from the earth bar to the biolers? or can it just be cross bonded with its pipe work?

the gas a water will be bonded in 35mm as the supply is 75mm 200A

as i say diffrent people have said diffrent things so just woundered what you think?:confused:

cheers
:cool:
chris
 
The heating pipework will only require main bonding if it is an extraneous part,.....see the BRB for definition,(the key phrase is 'liable to introduce a potential,normally earth').....reg 411.3.1.2 lists extraneous conductive parts which require main bonding and this includes central heating systems , this is where the confusion arises. A normal heating system is generally wholly within the confines of the equipotential zone apart from the boiler flu and thus is not liable to introduce an earth and so is not an extraneous part.
'Cross bonding' pipework outside of special locations is another example of those myths which have persisted for decades and result in an awful lot of unnecessary work..........if the heating pipes enter a special location they may require supplementary bonding otherwise there is no requirement for 'cross bonding' and there never has been.
 

Reply to earth bonding in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
161
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
997
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
3K
  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top