can some one help me as confused

a few people have said diffrent things about this

i am about to rewire a theatre building and it has 2 boilers, now do i need to have a main earth bond from the earth bar to the biolers? or can it just be cross bonded with its pipe work?

the gas a water will be bonded in 35mm as the supply is 75mm 200A

as i say diffrent people have said diffrent things so just woundered what you think?:confused:

cheers
:cool:
chris
 
The heating pipework will only require main bonding if it is an extraneous part,.....see the BRB for definition,(the key phrase is 'liable to introduce a potential,normally earth').....reg 411.3.1.2 lists extraneous conductive parts which require main bonding and this includes central heating systems , this is where the confusion arises. A normal heating system is generally wholly within the confines of the equipotential zone apart from the boiler flu and thus is not liable to introduce an earth and so is not an extraneous part.
'Cross bonding' pipework outside of special locations is another example of those myths which have persisted for decades and result in an awful lot of unnecessary work..........if the heating pipes enter a special location they may require supplementary bonding otherwise there is no requirement for 'cross bonding' and there never has been.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
earth bonding
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
djlander,
Last reply from
Deleted member 9648,
Replies
1
Views
1,656

Advert

Back
Top