gerard

Hi All,

I recently installed a new dist. board with 95mm sq 4 core swa cable. I used 35mm sq earthing cable even though I should have used roughly half the size of the live conductor. I used this because I had it, and was hoping it will be ok. I now fear that the cross section of the cpc. Is it possible to install an earthing point close to the new board to prevent me from installing a new earth cable?

Confused?!?
 
can you calculate for the armour and add that to the 35mm, see if it satisfies the adiabatic?
 
I could only terminate the swa on one end with a compression swa gland, access to the other side made it impossible so I just used a brass bushing. So, although it's a good idea, I can't use the armour. Any thoughts on another earthing point?
 
The armour needs earthing correctly but if you run a seperate earth that meets the csa needs of the sub mains then you only need to earth the swa at the supply end, but it still must be earthed regardless of the additional earth cable.
 
Hi All,

I recently installed a new dist. board with 95mm sq 4 core swa cable. I used 35mm sq earthing cable even though I should have used roughly half the size of the live conductor. I used this because I had it, and was hoping it will be ok. I now fear that the cross section of the cpc. Is it possible to install an earthing point close to the new board to prevent me from installing a new earth cable?

Confused?!?

I could only terminate the swa on one end with a compression swa gland, access to the other side made it impossible so I just used a brass bushing. So, although it's a good idea, I can't use the armour. Any thoughts on another earthing point?


I’m sorry Gerard. But all the above would be totally unacceptable to me!
 
Hi All,

I recently installed a new dist. board with 95mm sq 4 core swa cable. I used 35mm sq earthing cable even though I should have used roughly half the size of the live conductor. I used this because I had it, and was hoping it will be ok. I now fear that the cross section of the cpc. Is it possible to install an earthing point close to the new board to prevent me from installing a new earth cable?

Confused?!?

Had you terminated this 4 core 95mm SWA correctly, you would not have needed any separate CPC. The armouring would have been more than sufficient for your needs....
 
I do hope it's a cw gland.

By brass bushing I'm hoping its not just got the swa shoved through the hole in the panel.



edit:

I've seen it before so it wouldn't supprise me.
 
You can get liquid tight swa gland which is like a stuffing gland on the back of the swa gland to seal upto the sheath cw are not waterproof as many assume with their outdoor use.
Ive a feeling though this isnt the gland hes refering to.
 
Last edited by a moderator:
You can get liquid tight swa gland which is like a stuffing gland on the back of the swa gland to seal upto the sheath cw are not waterproof as many assume with their outdoor use.
Ive a feeling though this isnt the gland hes refering to.

Yes it's stated for outdoor use with cw glands, never seen a problem with properly fitted ones, even with a jet wash used to clean the plant down. The mistake most people make is over tightening the compression seal.

I have seen the ip65 swa glands, but I don't use them very often.
 
The swa is passed into the panel at one through a 50mm brass bush. I considered this OK under the circumstances as:
1. I would never have been able to fit a cw gland
2. the cable has no chance of moving as it is under ground, well supported, will never move and completely protected from people and elements.
My only concern is the size of the CPC, it is 35mm sq and the rule of thumb is half the size of live conductor. I do think the cpc is sufficient but I would be happier if it was say 50mm sq. So, my original question was - can an earth rod be installed near a new db to compensate for the undersized cpc?
 
In my opinion, there's not many places a gland can't be used. Even if you have to use the cone types with a jubilee clip like the ones found on some street lighting cut-outs. Not my favourite by a long shot, but would be better than not bothering at all.

As for the CPC, why can't the adiabatic be used? A 1 min calc, and you will be left in no doubt.
 

Reply to Earth Cable To Sub Distribution Board. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
893

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top