A
Alessandro
Hello guys,
I was hoping you could help me understand the following points!!
1.
Supplier says that Ze = 21 ohms. I test the earth electrode resistance (dead method) and get Ra = 72 ohms. Is Zs more or less = 72 + 21 = 93 ohms?
I know from Regulation 411.5.3 that that this should be true (d = delta): Ra * Idn <= 50 V.
I don't understand why, in the same Regulation, note 2 says: "Where Ra is not known, it may be replaced by Zs". I thought Zs should be at least Ze + Ra, am I wrong? Shouldn't I replace Ra with Zs - Ze?
2.
From Regulation 415.1.1: additional protection by RCD is Idn <= 30 mA, and operating time <= 40 ms at 5 times Idn. So my conclusion is that a current of 5 * 30 mA = 150 mA can flow for up to 40 ms. The maximum shock I can get is 150 mA for 40 ms? Isn't that quite a lot?
3.
In the continuity tests I keep reading that I should use a link at the CCU and disconnect bonding conductors, but isn't it a lot quicker and easier to use a connector block and connect, say, line and earth and test this closed loop at sockets / ceiling roses / switches etc? Why go through the trouble of disconnecting all sorts of things to avoid parallel paths?
4.
When the earth fault impedance tester is used for the earth electrode resistance test, I don't understand why my textbook says that it is less accurate. Wouldn't it be a lot more accurate, the values obtained being the actual impedance of the actual loop?
And then it goes on and says that this value is Zs. I thought it would be Ze? I am testing from the incoming line and the earthing conductor disconnected from the MET after all, we are not considering R1 + R2.
Thanks!
I was hoping you could help me understand the following points!!
1.
Supplier says that Ze = 21 ohms. I test the earth electrode resistance (dead method) and get Ra = 72 ohms. Is Zs more or less = 72 + 21 = 93 ohms?
I know from Regulation 411.5.3 that that this should be true (d = delta): Ra * Idn <= 50 V.
I don't understand why, in the same Regulation, note 2 says: "Where Ra is not known, it may be replaced by Zs". I thought Zs should be at least Ze + Ra, am I wrong? Shouldn't I replace Ra with Zs - Ze?
2.
From Regulation 415.1.1: additional protection by RCD is Idn <= 30 mA, and operating time <= 40 ms at 5 times Idn. So my conclusion is that a current of 5 * 30 mA = 150 mA can flow for up to 40 ms. The maximum shock I can get is 150 mA for 40 ms? Isn't that quite a lot?
3.
In the continuity tests I keep reading that I should use a link at the CCU and disconnect bonding conductors, but isn't it a lot quicker and easier to use a connector block and connect, say, line and earth and test this closed loop at sockets / ceiling roses / switches etc? Why go through the trouble of disconnecting all sorts of things to avoid parallel paths?
4.
When the earth fault impedance tester is used for the earth electrode resistance test, I don't understand why my textbook says that it is less accurate. Wouldn't it be a lot more accurate, the values obtained being the actual impedance of the actual loop?
And then it goes on and says that this value is Zs. I thought it would be Ze? I am testing from the incoming line and the earthing conductor disconnected from the MET after all, we are not considering R1 + R2.
Thanks!