Your question is not making sense to me. You don't need to calculate it if you are measuring it. If your measurement it is too high to give a satisfactory disconnection time against the tabulated rating for your protective device, then you should change either the bonding arrangements or use a different device. The only calculating you may need to do is adding or subtracting the loop tests at different points along the circuit to establish if and where best to introduce additional bonding if that is your chosen method of addressing the problem. You may wish or need to use R1+R2 for some of these measurements, but, at the end of the day, it is the Zs at the furthest point of utilisation that needs to be satisfactory.
If it isn't making sense you could call in an electrician for an hour or so and watch, ask and learn for less than ÂŁ40.