Basically this problem must have been present in the past , but there was no SEPAM unit on the old panel. Sorry i meant TNS suppy, Doh.
We have won the contract to do the swap over from new to old panels and re-test/certify the newly extended sub mains leaving the new panels. as all the DB's use HRC fuses as their feed, nothing has ever highlighted it previously . As i said earlier and i am glad to have had it confirmed by you the MRI scanner is a likely candidate so we are most definiteley going to be targeting that as one of the first things.
This is not the only supply to the hospital but one of 4, all the other supplies are on the new parts of the hospital we completed last year, their SEPAM relays are reading 0A , its just this old part of the hospital that is causing issues.
Nick
We have won the contract to do the swap over from new to old panels and re-test/certify the newly extended sub mains leaving the new panels. as all the DB's use HRC fuses as their feed, nothing has ever highlighted it previously . As i said earlier and i am glad to have had it confirmed by you the MRI scanner is a likely candidate so we are most definiteley going to be targeting that as one of the first things.