Earth fault loop impedance readings through a UPS supply | on ElectriciansForums

Discuss Earth fault loop impedance readings through a UPS supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

T

treak

Does anyone have any experience in recording values of EFLI on circuits fed through a DB supplied via a UPS please? The meter shows the above scale arrow.
I understand that there will be no reference to the external earth due to the inverter inside the UPS but what will happen to the UPS supplied circuits under fault conditions in normal supply mode? Is this something to be taken up with the manufacturer? Then there is next question how does the UPS deal with a fault in power failure mode? Not to worried about the second part, I obviously need to take some readings of EFLI to record and to see if they are sufficent to meet disonnection times.
Any help would be great.
 
You are only measuring the impedance of the output stage of the UPS.

Record values on bypass and remember that the UPS itself will clear any faults by limiting it's own short circuit current and eventually shutting down-often at around 100mS to protect the inverter and any damage downstream caused by the fault.
 

Reply to Earth fault loop impedance readings through a UPS supply in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K
If the shared neutral is lost ,won`t you be getting 400v across both cottages? 2 phase US style but double the Voltage.
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top