I have a my am2 practical testing exam next week and I'm confused about the earth loop impedance test.
The centre use a three lead instrument, I just want to know if this is right.

Connect the third lead to the neutral bar, and connect one lead to the earth bar
Then measure over the three phases L1 L2 L3 and record the highest reading

Cheers
 
Hi,

I have a my am2 practical testing exam next week and I'm confused about the earth loop impedance test.
The centre use a three lead instrument, I just want to know if this is right.

Connect the third lead to the neutral bar, and connect one lead to the earth bar
Then measure over the three phases L1 L2 L3 and record the highest reading

Cheers

At the origin, you do as you've already said but you need to connect directly to the earthing conductor, removed from the main earth terminal to eliminate any parallel paths.

For PFC, you need to measure worst case scenario so you leave all parallel paths connected, thereby causing a higher PFC.
 
My tester has the 3 lead cofig (it's a Metrel Easitest) When doing Ze, IR or continuity tests you plug the neutral lead into the top of the earth lead.
 
Thanks Guys,

So to carry out the test, using a 3 wire test instrument.

1.Disconnect the main earthing conductor
2.Connect one lead to the neutral bar
3.Connect the earth lead to the disconnected main earth conductor
4.Test over L1 L2 L3 record highest reading
 
Thanks Guys,

So to carry out the test, using a 3 wire test instrument.

1.Disconnect the main earthing conductor
2.Connect one lead to the neutral bar
3.Connect the earth lead to the disconnected main earth conductor
4.Test over L1 L2 L3 record highest reading

Spot on there.
 
Yea, I'm ok with that, just never used a three lead instrument before thats why I'm a little unsure

Well in my experience students often find using a 3 prong lead fairly simple, but sometimes get a little stumped when going from measuring the PFC to the PSC or vice versa.
 
Thanks Guys,

So to carry out the test, using a 3 wire test instrument.

1.Disconnect the main earthing conductor
2.Connect one lead to the neutral bar
3.Connect the earth lead to the disconnected main earth conductor
4.Test over L1 L2 L3 record highest reading

strictly speaking, in case they want to be awkward, you should also firstly switch off installation as well, as the rest of the installation is potentially not safe with the main earth disconnected.
 
Yea, I'd have the main switch at the D/B switched off.

Is there two ways of doing the test with a 3 wire instrument

1. Put the Green and Black leads together and connect them to the main disconnected CPC
2. Red lead,test over L1 L2 L3 record highest reading.

Or do I connect the third test lead to the Neautral bar?

Are both methods acceptable?

cheers
 
Yea, I'd have the main switch at the D/B switched off.

Is there two ways of doing the test with a 3 wire instrument

1. Put the Green and Black leads together and connect them to the main disconnected CPC
2. Red lead,test over L1 L2 L3 record highest reading.

Or do I connect the third test lead to the Neautral bar?

Are both methods acceptable?

cheers
The board you are testing will probs be backed with an rcd so you will probs have to do the "no trip" version which is with all three leads to separate points ie line , neutral and earth.

edit: or at least that is how it is with my tester
 
Last edited by a moderator:
The Tester I'm using is going to be a Megger MFT1552. (I think thats what they have at the centre)
I think you need to use 3 wires to carry out EFLP & PFC tests.
 
The Tester I'm using is going to be a Megger MFT1552. (I think thats what they have at the centre)
I think you need to use 3 wires to carry out EFLP & PFC tests.

that is what i have - it will do a 2 lead test but that will trip out if there is an rcd at the DB supplying the rig. So best be familiar with the 3 lead test :)
you set the meter dial to "no-trip".
 
The Tester I'm using is going to be a Megger MFT1552. (I think thats what they have at the centre)
I think you need to use 3 wires to carry out EFLP & PFC tests.

Yes, and it's depending on wether you can carry out the test on the high loop setting that will depend on your polarity. If it is high loop, and you have three leads.. I scanned this out of one of my books..
 

Reply to Earth Fault Loop Impedance Ze test at origin in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
267
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
762
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
752

Similar threads

FFS - popped it apart, found the same issue and thought I'd update... You guys were already there!
2
Replies
21
Views
2K
"When stoned..." Brilliant!
    • Like
Replies
6
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top