hello, i got this qustion and would like someone to show me the working out of it please.

the measured value of loop impedance for a circuit is 0.83 ohms. if the temperature at the time of the test was 20c and the cable is 70c (factor1.2), what is the correct value. ze = 0.4 ohms
 
your circuit resistance is multiplied bt 1.2 to allow for temperature. there fore, you would deduct the Ze from the Zs and adjust the remaining figure accordingly.
 
You cannot apply the correction factor to the measured value of loop impedance (Zs) as this includes the external loop impedance which is not subject to the 70c correction factor. So you need to subtract that from your Zs to give you your R1+R2 then apply the correction factor (1.2) then add the Ze back on.

The formula is:

= Ze + F(R1+R2)

Using your figures:

0.4 + 1.2 x 0.43 = 0.4 + 0.516 =0.916.
 

Reply to Earth Fault Loop Impedence question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
303
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
819
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
897

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
254
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top