Heres one. Over on another forum a poster has said that when doing loop tests they always test at the furthest point - which is correct, however they then go on to say that if they were testing a water heater circuit they would test at the connection point on top of the heater rather than at the spur / isolator.
From what I was taught when I was an apprentice, I was only taught to test upto the final connection point on the installation of the fixed wiring thus being the spur or isolator, and not to include the flex to the heater as that isnt part of the installation.
In effect if you go by the way this other person is testing you could say if you plug a 50M extension lead in then that would be the furthest point would it not, but in testing that your readings are going to be way out ? Take the immersion heater, 1.5mm HR flex - wired in 2.5mm t&e on the installation, two different cable sizes for a start, not a lot of difference in the resistance but surely that would be wrong to test that way.
From what I was taught when I was an apprentice, I was only taught to test upto the final connection point on the installation of the fixed wiring thus being the spur or isolator, and not to include the flex to the heater as that isnt part of the installation.
In effect if you go by the way this other person is testing you could say if you plug a 50M extension lead in then that would be the furthest point would it not, but in testing that your readings are going to be way out ? Take the immersion heater, 1.5mm HR flex - wired in 2.5mm t&e on the installation, two different cable sizes for a start, not a lot of difference in the resistance but surely that would be wrong to test that way.