yelloperil

I have recently fitted some lights in an attic and when I came to testing found the cpc showing 60 volts. I switched each mcb off in turn and the fault dissapeared when I turned off the downstairs lighting mcb. I am going back this weekend to sort the problem out so will start with an IR test. the house is only 10 years old and the customer has changed all the downstairs lights and switches.Is it fair to say that the fault should be on the downstairs lighting circuit?
 
On your minor works cert you only record the Zs value of the circuit that you have worked on.:)

Thanks pushrod.

What if I installed a new ring final circuit at the kitchen newerly buit in the same property above and only contains 5 sockets which connected directly to DB as a ring final circuit 4.

Q. Should I do all Zs testing for the circuits (1,2,3) to look for higher vale?
The reason I am asking is that the ring final circuit 4 would be much further distance than
other circuit.

Your answer gave me a lot of understandings and hope more.

JD
 
A new ring in the kitchen would have its own installation certificate (and is notifiable in a domestic property) - only test and record the results of the circuits you are working on unless you are doing a periodic inspection and test.
 
Thanks pushrod.

What if I installed a new ring final circuit at the kitchen newerly buit in the same property above and only contains 5 sockets which connected directly to DB as a ring final circuit 4.

Q. Should I do all Zs testing for the circuits (1,2,3) to look for higher vale?
The reason I am asking is that the ring final circuit 4 would be much further distance than
other circuit.

Your answer gave me a lot of understandings and hope more.

JD

I have a question for you jdtae,....do you understand the significance of the results of your Zs tests?...or put another way what are the results telling you?
 
I have a question for you jdtae,....do you understand the significance of the results of your Zs tests?...or put another way what are the results telling you?

In my understanding, it would be to see whether Zs value is low enough to let the current flow to operate the protective device in required time.
Can you please explain me if you see it defferently?

JD
 
I have recently fitted some lights in an attic and when I came to testing found the cpc showing 60 volts. I switched each mcb off in turn and the fault dissapeared when I turned off the downstairs lighting mcb. I am going back this weekend to sort the problem out so will start with an IR test. the house is only 10 years old and the customer has changed all the downstairs lights and switches.Is it fair to say that the fault should be on the downstairs lighting circuit?

You will find this is "Induced AC" in other words it is common to get 60-70 volts (picked up with a multimeter) on an earth that is not connected to the earth in the DB from a T&E due to the magnetic fields produced by the L&N. Once you earth it properly no more 60 volts.
This can also be a reason for false activations on burglar alarms as the cables a run along side mains cables and they also get AC pick up
 
A new ring in the kitchen would have its own installation certificate (and is notifiable in a domestic property) - only test and record the results of the circuits you are working on unless you are doing a periodic inspection and test.

Thanks again Pushrod.
I wonder if you can help me to clarify about the type of forms used for each cases.
1. Additional socket as a spur to existing ring final circuit.
-Minor electrical installation cert only or should I still fill the forms for Schedule of Inspections & Schedule of Test Results?
2. Same question for the newly added ring final circuit in the kitchen
(A new installation ring final circuit connected to DB)
I can understand that Schedule of Inspections & Schedule of Test Results should be accompanied by Periodic Inspection Report when carrying out Periodic Inspection.
But I believe that all three documents need to be filled in if I do Inspection and Testing for newly constructed building. - Would this be correct?
Just trying to tidy my head up which forms are to be filled in for the different circumstances.

JD
 
minor works only for the spur.

Electrical installation certificate, schedule of inspections and schedule of test results for the ring.

yes you are correct for the periodic inspection and test.
 

Reply to Earth Fault in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
247
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Oh dear, I missed the date!!!
Replies
6
Views
684
Any electronics in circuit that might be skewing the readings? Smokies. Or smart switches? Might have been covered already, but what about...
2
Replies
25
Views
807

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top