Gritishbasspark

Hi I have recently been asked to wire in a emergency 3 phase and N genorator in a work shop. I have a break before make change over switch, serge protection with a contactor incase of a spike on the genorator. The mains supply is a 3 phase and N TN-C-S system. What is trubbling me is what will I do with the earth. Due to the potentual currents on the neutral cable which in turn could come down the earth cable I don't want to connect everything to the supplys earthing system, but in that case my only opption is to put everything on to a TT system which isn't so great any ideas would be greatly welcome

David
 
Hi.


Well when the genny is running, assuming it is not a floating power supply (i.e. neutral isolated from earth in the genny?), the star point / neutral is connected to gen frame which is in turn earthed through the rod(s) you will have installed.;)

Think of a line to earth fault of a circuit supplied by the genny - the fault current will flow from the genny line, down through the circuit, through the fault, and will return through the SWA (or 3rd core) to the genny star point thus operating any protective devices in the geney. Generator outputs are by and large TN-S systems, because you are running an actual CPC in the cable, the fault current has no reason to go anywhere else other than back to its origin.

Any fault should not flow through the main supply earthing as they are not referenced together other than at their orgins via earth rods into the rock we all live on.

Likewise the rods on the gen frame ordinarily would not form part of the earth fault path of the geney system unless your installed CPC was damaged.

My opinion is to leave all earthing connected together as it is, with just the live conductors made or broken upon changeover.


My grey cells are pretty much dead for today now.....I hope this helps a bit.:)
 
And double check the neutral feed connection, especially so from 3 phase genny packs. I was once tasked with replacing lots of single phase appliances thet had fried because of this.;)
 
I agree with both of the above. Earthing is important and if you do not make a good neutral connection, Youy single phase circuits will have some unacceptable high voltages.
 

Reply to Earth for an emergency genorator set. in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Anywhere where the normal lights are dimmed or dimmable the emergency lighting should be of the maintained type. So maintained emergency lighting...
Replies
4
Views
981
davesparks
D
  • Question
Better/Smart/intelligent/expensive generators require two earth spikes set ~10-15m apart. They check the resistance between spikes and will...
Replies
5
Views
936
  • Question
Just re-read the OP's post and it is an existing 5C SWA so presumably a 3P supply. For 40A and 150m you are seeing 6.6V drop or 1.65% of 400V 3P...
Replies
8
Views
771
Not really its clear in black and white. Not knowing the regs isnt the regs books fault.
Replies
10
Views
758
  • Question
Good evening. Well done for beating Australia in the Rugby. To help you we need some more pictures and information on the overhead supply (ie...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks