Purpose
Many electrical installations have a relatively high
earth impedance. This may be due to the use of a local earth rod (
TT systems), or to dry local ground conditions.
These installations are dangerous and a safety
risk if a live to earth fault
current flows. Because earth impedance is high:
- not enough current exists to trip a fuse or circuit breaker, so the condition persists uncleared indefinitely
- the high impedance earth cannot keep the voltage of all exposed metal to a safe voltage, all such metalwork may rise to close to live conductor voltage.
These dangers can be drastically reduced by the use of an ELCB or
Residual-current device (RCD).
The ELCB makes such installations much safer by cutting the power if these dangerous conditions occur. This approach to electrical safety is called
EEBAD. In Britain EEBAD domestic installations became standard in the 1950s.
In non-technical terms if a person touches something, typically a metal part on faulty electrical equipment, which is at a significant voltage relative to the earth, electrical current will flow through him/her to the earth. The current that flows is too small to trip an electrical fuse which could disconnect the electricity supply, but can be enough to kill. An ELCB detects even a small current to earth (Earth Leakage) and disconnects the equipment (Circuit Breaker).
[edit] History
ELCBs were mainly used on
TT earthing systems. Nowadays, ELCBs have been mostly replaced by
Residual-current devices (RCDs). However many ELCBs are still in use.
Early ELCBs responded to
sine wave fault currents, but not to
rectified fault current. Over time, filtering against nuisance trips has also improved. Early ELCBs thus offer a little less safety and higher risk of nuisance trip. The ability to distinguish between a fault condition and non-risk conditions is called discrimination.
ELCB manufacturers include: Legrand,Havells,
ABB,
Siemens AG,
Areva T&D, TELEMECANIQUE, Orion Italia, Crabtree, MEM.