Sorry Hs,
I was sort of querying about these readings being imported, as you say it could be due to slight potential differences between the various different extraneous parts.
I suppose clamping the earth conductor on a TT system might give reliable indication of leakage currents in the installation, but I still think other installations nearby could introduce spurious currents via any shared services such as water and gas pipes and the like, Iam not sure.
As I say when I got my meter a couple of years ago I was playing about with it, as you do with a new toy, and it was quite disconcerting to see such currents on the earthing conductor, so much so I queried it with the DNO, but they did not see a problem (I worry too much).
So now I don't bother clamping the Earth at all.
Had it not been for that install already working fine and no RCD tripping, I too would have given a wide birth to doing any work on that install or similar, this is how I found out that clamping the Earthing conductor was a misleading test, and to just clamp the tails, I was just passing on the knowledge I gained to save people the trouble of thinking they had a problem when in fact it seems to be quite normal on some installs.
I would like to know more about this, and what is deemed unsafe limits of current on the Earth, for example does it have to be in the Amps or tens of Amps before it becomes a problem ?
Edit: I also clamped the main bonding conductors, as well as several CPC's and registered nothing of any note (0 mA), this was the other reason I felt it was due to external means beyond my control.
Edit II: I have just clamped the tails here, and registered 7.8 mA, I clamped the Earthing conductor and got 7.1 mA (it is on a TNS system), but as I say on some installs the Earth can measure quite a larger current, which is why I said it is not a reliable test clamping the earthing conductor, I wonder if it depends on the earthing system (TNC-S ?), or if some nearby installs had earth faults, or maybe even electrical noise ?