Hi all

does any ony know what earth leakage a computer gives.
as i have a site which will have only a few computers all cable are flush and customer wants a few additional sockets.
543.7.1.3 is for circuit with 10mA of leakage,

also if so can you clarify

543.7.1.3(i) a 10mm earth conductor i asume this is intended for sub mains
543.7.1.3(ii) run 4.0mm additional ring terminated in seperate terminal in each accessory
543.7.1.3(iii) use of and 4.0mm earth inside metal conduit or if swa L+N+E to equal 10mm

if this is correct i would go with the 4.0mm ring but i is going to be a pig as the place if flush and has no additional earth installed
 
I think the average computer has an earth leakage of about 3.5mA. This would appear to indicate that you can have up to 8 computers on a circuit without tripping the RCD, however many 30mA RCDs actually trip well below 30mA, some as low as 10mA.
(i)The requirement for the 10mm² protective conductor applies both to final circuits (i.e. ring mains) and distribution circuits (i.e. sub mains), this is for when the conductor is not copper.
(ii)Where there is a single copper conductor (i.e. just the one), it must be not less than 4mm².
(iii)You can use 2 protective conductors that when added together are less than 4mm², as long as each conductor meets the requirements of Section 543 (i.e. each CPC either satisfies the adiabatic equation or is selected in accordance with Table 54.7). The conductors do not both have to be copper, one could be metal conduit and the other the CPC of T&E.
I'm not certain what you mean by flush?
Anyway, you have a number of options, you can wire the circuit in 2.5mm² singles using a 4mm² CPC, or two 2.5mm² CPCs, you can use 2.5mm² singles with an extra 2.5mm² CPC, you can use 6mm² T&E as long as the CPC is 4mm², you can use metal conduit with 2.5mm² T&E and the condit as the extra CPC or even just 2.5mm² Line and Neutral conductors and the Conduit as the only CPC.
Remember that any CPC less than 4mm² has to be mechanically protected, and if two CPCs are used then the socket-outlets have to have two connection terminals one for each conductor.
 
Last edited by a moderator:
thank you all

so in my situation the existing is T+E
so if i run a 4.00 around to each socket installing these in to a seprate terminal in each accessory as a radial this is as stated it does'nt need the 4.00 run in a seperate ring and terminated in the seperate terminal
 
thanks
543.7.1 states 60309-2 socket but i find no menchon of bs1353 which 543.7.2.1(i) states must comply to 543.7.1

I have all way done it with 4.00 ring twin termeinal ect but i have to put down compliants to which regs but cant see how 13A sockets will comply now why cant the regs be more clear
this is turning in to a time consuming job
 
BS EN 60309-2 refers to industrial plugs and sockets, to be used on equipment where the earth leakage is between 3.5mA and 10mA.
BS1363 plugs and sockets are acceptable where the earth leakage is anything up to 3.5mA.
 
Beaver, the file I posted covered this topic well, including ways of terminating the cpc's to comply with the requirements of installations with high protective conductor currents:

It's one to keep in your technical folder as this subject is so misunderstood!
 

Attachments

  • High Integrity Earthing.PDF
    485.8 KB · Views: 220
with the risk of starting a long thread of aposing views i have found a lot of threads where the way of wiring is not agreed on .
i have alway been told that with twin and earth the 1.5 earth is done away with and the 4.00 earth is installed connected in seperate terminals through out in a ring.
but there are also views of the 1.5 ring should be terninated in 1 terminal 4.00 in a seperate 1 giving 4 earth conductors in each accessory .so having 2 rings .what is the correct way
 
It's not really 4 conductors at each accessory, 4 cables for 2 conductors.
But yes that is how it should be wired the cables of one conductor in one terminal, the cables of the other conductor in the other terminal.
The reason why some people do away with the 1.5mm² CPC, is because a single 4mm² conductor is all that is required, and normal socket-outlets can then be used.
 
According to the on site guide (Red book page 67) 7.6.3 reg 543.7.2.1. A ring final circuit wired in T+E with 1.5mm
earths is adequate, as long as dual earth sockets are used and earths are split at the db
 

Reply to earth leakage of a computer in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top