a friend of mine told me he uses the clamp meter for his ir tests dosent do any ir testing just calculates the ir from the leakage current he detects whats your thoughts on that says it saves him lots of time still need convincing that this is ok

I use that method on jobs where I need to know the ir but can’t turn the power off
 
a friend of mine told me he uses the clamp meter for his ir tests dosent do any ir testing just calculates the ir from the leakage current he detects
Does sound dodgy ,if no one else can get same figure with 500V .
Can see where he is coming from Not having to unplug all those delicate electronics (they get tested at 380-400VDC)
 
Wot I need power factor in my clamp meter ?
Not sure what you mean?

So if using an EL clamp to calculate IR you would be calculating the impedance as the insulation has a capacitive reactance..
We use dc voltage to measure just the resistance and the capacitive component is ignored.
 
So if using an EL clamp to calculate IR you would be calculating the impedance as the insulation has a capacitive reactance..
Insulation impedance (including capacitive reactance that could raise current ,but not power consumption... Hence appearing a little lower Z than actual R.
Was hoping for some amazing science ,(but with only the current -It cannot know the phase of the voltage to {filter-out} capacitive part of current )
Not to matter.
 

Reply to earth leakage in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Not a reliable indication of a fault! What RCD characteristics (and also why is an incomer needed here)? Have you done a global L+N IR test to...
Replies
6
Views
925

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top