Had a strange one today, would appreciate folks take on it. I'm probably missing something obvious!!
Installing some downlights via metal dimmer switch.
Earth loop impedance was 50 ohms at last light!, at switch it was about 1.5 ohms. Dimmer fully up, voltage at light around 230 . Bypass switch and readings come down to 1.8 ohms.
Why would a dimmer cause this?, anyone else come across this ? Am I being a total idiot ( probably!!, it's been a hard week!)
Thanks in advance for any advice.
 
dimmer electronics will throw your readings down the pan. need to be bypassed for efli testing and IR tests.
 
Thanks folks.
My confusion is, if I test without the switch and get 1.8 , but when switch is fitted it's nearer 50, what is the true reading ?
When the switch is fitted , is the true ELI 50 ohms or is that just a misleading result .? I hope I'm making sense here.
Thanks again, much appreciated.
 
Thanks folks.
My confusion is, if I test without the switch and get 1.8 , but when switch is fitted it's nearer 50, what is the true reading ?
When the switch is fitted , is the true ELI 50 ohms or is that just a misleading result .? I hope I'm making sense here.
Thanks again, much appreciated.
Your bog standard dimmer switch only lets current through on part of the cycle, it is effectively chopping it which reduces the RMS current hence it "dims".
Your tester will not cope with this and will either give no reading or a false reading. Under a fault condition the internal triac should fail and allow this fault current to flow and hopefully trip the OCPD. Be careful doing EFLI tests through a dimmer as this can also damage the triac. So your reading of 1.50 is correct.
 
easy enough to check. bybass the switch with the circuit de-energised then get a R1+R2 reading.
 

Reply to Earth Loop / Dimmer in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
959
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Hello What was the conclusion of your problem?
Replies
1
Views
826
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top