Then your tester is wrong .............it is one thousand six hundred and sixty seven ohms.
Are you sure the tester is not woried as to why there may be a a high value? Not seeing the installation, but for a socket circuit that does seem high unless it is a very long socket circuit.
Though it is well with the RCD capacity, you may want to check why there is such an high Zs value.
What we have to take into account is how he tested them, was it a measured Zs, or as he done the R1+R2 and calculated it. Sometimes on sockets when doing a LIVE test for Zs the socket outlet you try on can give you a high reading, due to perhaps dirty terminal prongs, often on testing if I got an higher than expected result I would remove and insert the plug a few times and re test.
If I was still getting a high value then you may have to look at perhaps a loose connection somewhere.
Tohugh the RCD will operate it is best to find out why something is not as it should be