Hello I would like some help understanding the earth loop test.
I'm only training at the moment but I recently had the opportunity to pick up some testing kit very cheaply so thought I'd give it a whirl as I could then experiment at home getting my head round some of the tests. The insulation test and low ohmic meter seem to be ok from a little experimentation. Not tried the RCD tester yet.
First as I understand it the the earth loop test measures the impedance along the phase to the supply transformer then back though the earth to the point at which the tester is plugged in. I guess this is the Zs of that socket / fused supply point e.t.c.
Please correct me if any of these point are incorrect.
I am also guessing that it obtains this measurement allowing a small current to pass between phase and earth. A friend tested the installation last week with his kewtech and obtained a reading of 15.1 Ohms, apparently still within regs with the limit being 22.0 ohm for TT. Is this correct? (The ground is stony and very dry at the moment).
The earth loop testers is a Di log Lt22 the instruction with the meter refer to the 15th edition regs (see pic). The system I am testing is a TT system. The CU is an old Wylex.
The problem I have is that when ever I try and use the tester the RCD trip out. Is this just because for some reason the loop tester is allowing too large a current to flow between phase and earth, hence RCD tripping? Dose this mean the test is broken? The instruction just say select 0-10 ohms, plug in, check LN and LE neons illuminate, press test button for reading.
I just thought maybe I should be trying 10 -100 ohm to get a reading as I'm on a TT system but if it's tripping it's tripping regardless of if I am managing to get a reading!
Sorry for the long post, I'm just getting my head around some of this testing. Thanks for any help.
I'm only training at the moment but I recently had the opportunity to pick up some testing kit very cheaply so thought I'd give it a whirl as I could then experiment at home getting my head round some of the tests. The insulation test and low ohmic meter seem to be ok from a little experimentation. Not tried the RCD tester yet.
First as I understand it the the earth loop test measures the impedance along the phase to the supply transformer then back though the earth to the point at which the tester is plugged in. I guess this is the Zs of that socket / fused supply point e.t.c.
Please correct me if any of these point are incorrect.
I am also guessing that it obtains this measurement allowing a small current to pass between phase and earth. A friend tested the installation last week with his kewtech and obtained a reading of 15.1 Ohms, apparently still within regs with the limit being 22.0 ohm for TT. Is this correct? (The ground is stony and very dry at the moment).
The earth loop testers is a Di log Lt22 the instruction with the meter refer to the 15th edition regs (see pic). The system I am testing is a TT system. The CU is an old Wylex.
The problem I have is that when ever I try and use the tester the RCD trip out. Is this just because for some reason the loop tester is allowing too large a current to flow between phase and earth, hence RCD tripping? Dose this mean the test is broken? The instruction just say select 0-10 ohms, plug in, check LN and LE neons illuminate, press test button for reading.
I just thought maybe I should be trying 10 -100 ohm to get a reading as I'm on a TT system but if it's tripping it's tripping regardless of if I am managing to get a reading!
Sorry for the long post, I'm just getting my head around some of this testing. Thanks for any help.