Peter Hartley

Hi there Guys

I am new to the UK and have just a quick question. When your earth loop reading I too high in the UK, can you proceed to do an earth/neutral bond before the consumer main switch or do you have to contact the applicable power utility company?
 
Thanks Guys. I was talking about the external loop, however I have established that in the UK the DNO is responsible for that cable and I will just alert them. Yes PEN conductor is illegal after the customer point of control. In SA the DNO stops at the meter in the kiosk outside the property. Therefore you have a cable feeding the installation from the meter to the point of control. Sometimes the earth on this cable deteriorates and a earth/neutral bond is then made in order to restore a proper earth.
 
Thanks Guys. I was talking about the external loop, however I have established that in the UK the DNO is responsible for that cable and I will just alert them. Yes PEN conductor is illegal after the customer point of control. In SA the DNO stops at the meter in the kiosk outside the property. Therefore you have a cable feeding the installation from the meter to the point of control. Sometimes the earth on this cable deteriorates and a earth/neutral bond is then made in order to restore a proper earth.

Even in that scenario it would be unacceptable to make such an earth/neutral link. If the earth conductor has deteriorated then the cable is damaged and must be replaced (or repaired if possible)
 

Reply to Earth Loop too High in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
Hi Mike, Floating Neutral. I'm really over simplifying below, but using generators as an analogy is possibly easier to understand. In a large 3...
2
Replies
23
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top