Here we go for my first post.

I have been working as an electricien for 25 years

This may cause some discussion?

With reference to Earth loop values in the Bible.
Has any one ever contacted the manufacturer of MCB’s to enquire to the specific loop values they publish? You may be surprised to find that they are higher values than the Bible.
Now the question is can you go by these values.
 
Hi Steve and welcome.

Good question, one of which like you say, may cause a few heads to hurt.

Typically, as you know, manufacturers instructions generally over rule the BRB, however im not sure on technical details over ruling.

Would be interesting to hear what others opinions are.
 
Hey Steve, welcome along.:D

Personally I go by the BRB as on the forms it asks for max permitted by BS 7671 not by Merlin or Hager or Wylex etc.

Also if the book values are lower then that can only be a good thing surely.

[ElectriciansForums.net] Earth loop values


P.S I have my tin hat on!!!!:D
 
Quite right lenny however if the disconection times are achieved with higher Loop readings can this not prevent a lot of costs especially on periodic's if this was noted on the report.
As for new works this should be designed in with Ze in mind.


I like the one's that make you think.
 
Hi.

Agreed, on new installations there is no excuse for failing to comply with max values for Zs as full consideration should have been given in the design stage.

I see what your saying with regard to the periodic on an existing installation scenario, but again I'm drawn to the whole "to BS7671" quote. Worst case scenario would be having to change an MCB for an RCBO. Agreed, there is extra cost involved but I think it would niggle away at me if I didn't because the Zs still complied with manufacturers spec.

It's a tough call but I would deffo advise the client on addtional RCD/RCBO protection if the Zs fell outside of BS7671 values on an existing installation.

Cheers.
 

Reply to Earth loop values in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

  • Question
Hi I'm again struggling with a long overdue 2396 project but, as before, am at a standstill when it comes to the lighting design. Please could...
Replies
0
Views
661
Concerning isn't it. I fear it's just going to lead to reduction in standards and entry requirements and flood the industry with even more poor...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top