M

matt12321

the maximum tabulated value of earth fault loop impedance for a circuit 1.85 ohms. if the resistance of the line and cpc of a new circuit is 1.03 ohms. whats the maximum accepted external earth loop impedance value
 
As your Zs = (R1+R2) + Ze you can work it out, transpose by subtracting (R1+R2) from both sides of the equation:

Ze (Max) would be Zs - (R1+R2)

Which would give you 0.82 Ohms max
 
Upvote 0
Be a little cautious when you see the word tabulated though, if you're dealing with current cable limits you'll find that the values in the on site guide are 80% of those in the BRB. See what the question is asking for as to whether you need to adjust the values you're given or not.
 
Upvote 0
Just think about how the resistance of the fault path is made up. Ze = external, external to the circuit under test. The R1+R2 value is the total resistance of all the line conductor in series with the CPC (ie the maximum resistance if the fault was right at the end of that circuit (it'll typically be less than that but you use the worse case scenario for safety)). HTH.
 
Upvote 0

Reply to earth loop in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
He is after the four options for 1 and 2 of the multiple choice exam, probably optimistic someone will know this. Your question 3 in incomplete to...
Replies
2
Views
1K
  • Question
When I did my AM2, I had it drummed into me that I had to follow Guidance Note 3 carefully. So, did you follow the guidance in GN3 for checking...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top