lsdweb

I popped round to a friend's house as his RCD is tripping occasionally - it's a 15th Edition board with one RCD covering all circuits so pretty annoying.

I thought I'd start checking to make sure there was a good earth and was surprised when the Ze came out at 120 ohms - as I assumed the supply would be the same as mine (next door) ie PME / TNCS. When I opened the meter cabinet, I saw this [ElectriciansForums.net] Earth Loop.

The house was built by a plumber I think and maybe he took the words "earth loop" too literally!

The cable comes from the main earthing terminal, loops through the cabinet and disappears down through the cavity. I've had a hunt around and can't find an earth electrode and I doubt there's much structural steelwork in the ground for this to be connected to.

Anyway, it now has a proper connection to the PME supply with a Ze of .25 ohms.

W
 
Looks like the house is still on the 'temp supply' from when it was being built.

Chances are, there is an earth rod buried away somewhere as the DNO wouldn't power up the head on a new build or let you use their earthing system until the house was finished and certified. To have power on site to work with, you had to provide your own temporary earthing system and when the house was finished you contact DNO and they come out and give you the permanent supply and connection to their earthing system.

Looks like a phonecall is needed.
 
Looks like the house is still on the 'temp supply' from when it was being built.

Chances are, there is an earth rod buried away somewhere as the DNO wouldn't power up the head on a new build or let you use their earthing system until the house was finished and certified. To have power on site to work with, you had to provide your own temporary earthing system and when the house was finished you contact DNO and they come out and give you the permanent supply and connection to their earthing system.

Looks like a phonecall is needed.
Yes and a schedule of tests Ze Zs etc as the supply characteristics have been altered here now
 

Reply to Earth Loop in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
310
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
933

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
950

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top