I've just done an EICR on an install earthed TT . The Ze on the rod was high 245 ohms , which in theory is fine as it is less than 1667 and the equation Ra X 0.03 > 50v is satisfied .
When the gas and water bonds are reconnected the Ze drops down to 4.4 ohms ,

Do I put another rod in ?
The property is in a built up area with pme available , do I get the Dno to fit pme ?
 
it's the gas and water pipes bring down the Ze. rather than relying on that, a PME system would be advantageous.
 
Yes an enquiry for pme would be worth it if the customer fancies the outlay. The measured ze would be worth a mention on the report, as would the less than desirable situation of RCDs providing fault protection where a viable and more reliable alternative exists.
 
The rod resistance shouldn't exceed 200 ohms. It is nearly always the case for it to drop with the bonding connected due to parallel paths. This resistance could even increase in the drier months so yes I would try to look at PME.
 
Earthrod is unstable you can't rely on the fact that gas and water pipe bonding brings tears resistance down as metallic pipes may be replaced in future with plastic equivalents. Either install new rod or tnc-s enquiry
 
The rod resistance shouldn't exceed 200 ohms. It is nearly always the case for it to drop with the bonding connected due to parallel paths. This resistance could even increase in the drier months so yes I would try to look at PME.

For what reason should it not exceed 200 ohms?
 
If 200 ohms is stable, much better than the ra all over the place,with an earth to earth system which TT is, stability is key.
 

Reply to Earth rod and bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

  • Solved
There is an article about that here: https://www.cement.org/learn/concrete-technology/durability/corrosion-of-embedded-materials It states...
2
Replies
27
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
929

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top