So we all know that the regs say that a TT systems Ze should be below 200 Ohms as anything above could be unstable.
My question is when installing an earth rod throws up results higher than 200 ohms, say 300 or 400 ohms, what is the point really in installing secondary/tertiary earth rods?
I recently rewired a TT installation and was called out by my Elecsa assessor on my assessment visit because the Ze was 212 ohms. He asked if I was planning on whacking another rod in to which I replied "no".
He spent some time questioning me over the issue whilst I basically explained to him that I couldn't see the point. In short, the earth rod was in the best possible position to reduce the likleyhood of fluctuating resistance values however the ground conditions surrounding the property were so bad that I'd have had to probably whacked in another two or three throughout the customers rather small garden to have even stood a chance at bringing it down to a more reasonable 100 ohms and even then, what would be the point. The fact is I'd have needed a Zs of 1.44 ohms for ADS to operate within 0.4 seconds during earth fault conditions and that is just never going to happen. We rely on RCD's in TT installations (rightly or wrongly) which allow us a permittable Zs of 1667 ohms anyway.
Anyway, after our conversartion, the assessor seemed more than happy with my reasoning and was happy with the installation but my question is, who came up with this 200 ohm figure in the regs and why? I mean I know it's a guide, but why 200 ohms? 300 ohms would be just as meaningless, as would 1 kohm or alternatively 20 ohms.
Tin hat on for the whole 212 ohm thing
My question is when installing an earth rod throws up results higher than 200 ohms, say 300 or 400 ohms, what is the point really in installing secondary/tertiary earth rods?
I recently rewired a TT installation and was called out by my Elecsa assessor on my assessment visit because the Ze was 212 ohms. He asked if I was planning on whacking another rod in to which I replied "no".
He spent some time questioning me over the issue whilst I basically explained to him that I couldn't see the point. In short, the earth rod was in the best possible position to reduce the likleyhood of fluctuating resistance values however the ground conditions surrounding the property were so bad that I'd have had to probably whacked in another two or three throughout the customers rather small garden to have even stood a chance at bringing it down to a more reasonable 100 ohms and even then, what would be the point. The fact is I'd have needed a Zs of 1.44 ohms for ADS to operate within 0.4 seconds during earth fault conditions and that is just never going to happen. We rely on RCD's in TT installations (rightly or wrongly) which allow us a permittable Zs of 1667 ohms anyway.
Anyway, after our conversartion, the assessor seemed more than happy with my reasoning and was happy with the installation but my question is, who came up with this 200 ohm figure in the regs and why? I mean I know it's a guide, but why 200 ohms? 300 ohms would be just as meaningless, as would 1 kohm or alternatively 20 ohms.
Tin hat on for the whole 212 ohm thing