Had to fit 2 earth rods to TT 2 adjacent buildings.
The only available soft ground was a approx 3 foot gap between the two buildings.
I have spaced the rods a good distance from each other, but could someone point me in the direction of the regs to do with spacing between the rods for use in my report.
Ta.
 
Do the UK regs actually specify a spacing distance? We try to keep rods 10 meters apart as a rule, sometimes less than half that distance is sufficient, sometimes not it depends greatly on the make-up of the ground, the height of the watertable and many other factors that don't remain constant from location to location
 
Spacing of earth electrodes are generally based on the length/depth of the rods used... if 3 metre rods used, then a space of not less than the 3m length must be provided. This is so that there is little chance of any overlapping of the rods areas of influence. It is also recognised that there is little benifit if any, in exceeding 1.5X the rod length spacings...
 
FIG 2.6..GN3..(P47)
shows temporary spikes placed 6 meters either side of T2 which itself is 15-25 meters from the electrode under test.
542.2.2 GN3 also quotes in paragraph 4 that the test spike (T1) is at least 10 times the maximum dimention of the electrode system, e.g. 30m for a 3 m long rod electrode.
 
I think it went up from 3 meters (16th)...to 6 meters (17th) but this may just be placement of spikes for testing..........

That doesn't sound like even test spike distances...lol!!! Most of the test manufacturers kit that i have used, generally ask for between 20 to 50m to the current test spike, and 10 to 25m for the furthest potential test spike!!

EDIT ...Anyway were talking about distances between driven earth electrodes, ...not earthing test kit spacings of test spikes...
 
Last edited by a moderator:

Reply to Earth Rod Spacing in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
780
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
789

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
947
  • Question
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
Replies
2
Views
482

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top