uksparks
-
3 months ago I sunk in 3 rods, two were 4m deep and the other 3m deep, Ra achieved at the time was 3.1 ohms using a Three lead spike test kit.
i hooked the summerhouse up today and finished it off,
i measured Ra again and it was 2.5 ohms, then just to let you know how close it was to Ze, so accuracy of the spike test, Zdb at the new board came out at 2.88 ohms, that was on the end of a 52m run of 16mm SWA.
im very happy with the end result.
i hooked the summerhouse up today and finished it off,
i measured Ra again and it was 2.5 ohms, then just to let you know how close it was to Ze, so accuracy of the spike test, Zdb at the new board came out at 2.88 ohms, that was on the end of a 52m run of 16mm SWA.
im very happy with the end result.
Last edited: