Earth size in flat cable | on ElectriciansForums
Discuss Earth size in flat cable in the Australia area at ElectriciansForums.net
Manchester
Please excuse my ignorance my professional comrades but i am completing a schedual of test results and am not sure of the earth size in 1.5mm, 2.5mm an 4.0mm cable. If someone would be so kind as to enlighten me i would be very gratefull and promise to thank you with a click of the thank button!!!!!
are these test results part of a college exercise?...or for an actual install?......
Standard T+E Sizes:
Line (mm[SUP]2[/SUP]) CPC (mm[SUP]2[/SUP])
1 ------------1
1.5 ----------1
2.5 --------- 1.5
4 ----------- 1.5
6 ----------- 2.5
10 ---------- 4
16 ---------- 6
Note: Be aware up to 3 CPC size options are available from the cable manufacturers for most T+E cable sizes, however, mostly encountered in commercial or industrial installations.
OSG Appendix I, Table 11.
Reply to Earth size in flat cable in the Australia area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...