At my place of work we are about to run a 3 phase supply from the main factory out to an office building (brick-built, not temporary). We are using 35mm 4 core cable running through underground pipework for around 40 meters. The factory has a TN-C-S earthing system and we were anticipating running a separate earth cable parallel to the main cable. However, an electrician has advised us that as it’s a separate building it must (a) be provided with a TT earth electrode, and (b) the TT earthing system must be isolated from the TN-C-S system. Now I had no problem with the need for a TT earth electrode - although a quick look around some forums indicates this is probably not a requirement, and we probably could have had a continuation of the TN-C-S without problem. But my main question is that other than for initial testing purposes, why would the two systems require absolute isolation? Once their initial integrity had been proved, surely neither could compromise the other? And the greater the number of paths the earth in a fault situation the better? I can find nothing in the 17th to support either claim – though I could have missed it. Some clarification would be appreciated.
Cheers,
Phil
 
Why not run a 5 core and use the TNc-s supply

TT should be isolated from the Tnc-s because the earthing and bonding of the outbuilding would need to meet the requirements of Tnc-s earthing and bonding if they are linked and not TT requirements
 
Is this building going to have it's own services such as water for toilets, kitchens etc, or are you going to bring the services from your existing building.

If your going to utilise services from the main building then the electrician may have recommended a TT system becasue these services will need to be bonded back to your main building MET which is 40 metres away. By utilising a TT you can create a completey seperate equipotential zone and thefore bond the services at the local board.

You could though run a 5 core cable 35mm and use the extra conductor for the bonding and the SWA as your CPC.
 
The building has been in use for several years. It has got a water supply installed for toilets, kitchen etc. although these aren’t taken directly from the factory building. The existing single phase supply isn’t up to the increasing demands, so it was decided to upgrade the system. We were actually thinking of using SY rather SWA as the route requires some flexibility, and 35mm SWA will have some problems with the available radius. Although we can get the SY in 5 core, I don't think the braiding would really pass should it be considered part of the earth system; hence the separate earth wire comment. Economy-wise it may well be cheaper to install a separate TT system, but my curiosity centered on the 'requirement'? to isolate the two earth systems should that scenario arise.
Many thanks for the replies so far
Phil.
 
Unless your going to be prepared to make a decent deep driven rod installation, then stick to the TNC-S earthing system.

As this is a place of work, it's not going to be the same as your typical outbuildings rod installation, and the cost equation between rods and bonding conductor, could well be in favour of providing the bonding conductor. Besides why ditch a perfectly good earthing arrangement, for a more than possible lower one??

Find out from the cable manufacturer, the CSA of the braiding provided on the SY cable your proposing to use.

EDIT.... The separate core of the cable is for your bonding needs, the braiding of your SY cable will if of suitable CSA will be your CPC, no problem both being connected to the MET of the CU/DB at the load end. If your using a 5 core cable, the CSA of your braiding is going to be increased, and may well be more than adequate for your CPC needs....
 
Last edited by a moderator:

Reply to Earth system clarification in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
800
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
983

Similar threads

In TN-S systems, you shouldn't isolate the neutral in a 4-pole isolator. Connecting neutrals to a dedicated terminal is acceptable and safe...
Replies
4
Views
787
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top