G
Guest111
Hi all,just after a few thoughts on this one been to look at the place I used to work at and they are having a new building put up,I had to straighten out the wiring last time after the previous spark had made a b of it and had not bonded the steelwork which I did.Now they are having a new shed put up,concrete panels and steel beams next to the existing one,you can stand between the 2 and touch both sets of steelwork so the question is do you tt second building or do you bond back to main earth in first building? I know the regs about not exporting pme but it concerns me if someone were to touch both sets of steel at same time could there be a difference in potential between the 2? the supply is a tncs system 3 phase.seems funny asking for advice on this as I am usually advising others but just thought I,d run it by you guys.nice little job to do in my retirement lol.