K

Ken77

Hi,

I have done a E.I.C.R report on an installation with 16mm meter tails and 6mm Earth conductor. Whilst this is undersized and should be 10mm, using the adiabatic equations the 6mm is fine to carry the fault current. My question is this, the bonding is also 6mm and whilst I would recommend for this to be upgrade to 10mm, would you class this as unsatisfactory and fail an installation? As the bonding is present (albeit undersized) would you code this as C2 or C3?

Thanks
 
what earthing system is it? if it's TT or TN_S then a code C3 would be appropriate as long as no signs of thermal damage.
 
you do. with TN-S the bonding conductor needs to be 50% of the csa of the main earthing conductor with a min. of 6mm. as long as the adiabatic confirms that the MEC is adequate, you're OK. however, i'd be inclined to upgrade the MEC to 10mm or 16mm if it was an easy job.
 
Ken, if you've confirmed the MEC is ok at 6mm then it's not undersized is it? If a TN-S then the main bonding is also ok at 6mm. No code is warranted, not sure why you would reccommend unneccesary work?
 
Hi,

I have done a E.I.C.R report on an installation with 16mm meter tails and 6mm Earth conductor. Whilst this is undersized and should be 10mm, using the adiabatic equations the 6mm is fine to carry the fault current. My question is this, the bonding is also 6mm and whilst I would recommend for this to be upgrade to 10mm, would you class this as unsatisfactory and fail an installation? As the bonding is present (albeit undersized) would you code this as C2 or C3?

Thanks
As long as the adiabatic equation says 6mm is ok then its fine, but I agree with telectrix in regards the MEC, unless its a hard job, change to a 16mm, no question
 
I agree, if the tails are adequately protected by the suppliers fuse, then they are ok, no code despite what people say.
on a TT or TNS the earthing conductor can be sized using the adiabatic, and the bonding is half of that, with a minimum of 6mm.
again no code.
the problem is that other sparks who follow will almost certainly slate it. A little knowledge and all that.
 
Belt and braces, how long is it gonna take? how much will it cost? I know its not required to be upgraded but that's the way I work and that's what ird always recommend

Fair enough, I'm not 'avvin a pop but I just don't understand why you'd fix something that aint broke.

What would you explain to the customer if you were to reccommend upgrading a perfectly adequate 6mm earthing conductor to a 16mm one and they asked why? What if they were to ask you why you were reccommending fixing something that aint broke?
 
Fair enough, I'm not 'avvin a pop but I just don't understand why you'd fix something that aint broke.

What would you explain to the customer if you were to reccommend upgrading a perfectly adequate 6mm earthing conductor to a 16mm one and they asked why? What if they were to ask you why you were reccommending fixing something that aint broke?

It wouldn't be a job ird quote and charge for, ive done things like this before and not even mentioned it to the client, it wouldn't even require a conversation but if it did and if someone's paying me for my professional opinion im gonna tell them exactly what I think, regardless of what the "regs" say, they're only for guidance, they way I carry out my work is based on a combination of what the regs say, my experience and the kind of organisation I want to be proud of running. that is of course assuming its a basic short length of cable that just needs replacing which lets be honest, it usually is.
 
It wouldn't be a job ird quote and charge for, ive done things like this before and not even mentioned it to the client, it wouldn't even require a conversation but if it did and if someone's paying me for my professional opinion im gonna tell them exactly what I think, regardless of what the "regs" say, they're only for guidance, they way I carry out my work is based on a combination of what the regs say, my experience and the kind of organisation I want to be proud of running. that is of course assuming its a basic short length of cable that just needs replacing which lets be honest, it usually is.

Fair enough, I still don't understand why but I accept what you're saying and I'm not going to condemn it.
 
The trouble is that if you replace the EC with 16 - 'just because you do' - someone else is going to come in and state that the MPB should be 10 and that could be a pita to fit costing the customer.

It's the same as replacing tails with 25 - 'just because you do'.

It isn't necessary and achieves nothing.
 

Reply to Earthing and bonding arrangements in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! âš¡ Please note that all EV Chargers and...
Replies
0
Views
117
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
910
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
Any metalwork connected to the MET could rise in voltage compared to true earth under an open supply neutral fault (on TN-C-S), and that would...
2
Replies
24
Views
2K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top