I have done a E.I.C.R report on an installation with 16mm meter tails and 6mm Earth conductor. Whilst this is undersized and should be 10mm, using the adiabatic equations the 6mm is fine to carry the fault current. My question is this, the bonding is also 6mm and whilst I would recommend for this to be upgrade to 10mm, would you class this as unsatisfactory and fail an installation? As the bonding is present (albeit undersized) would you code this as C2 or C3?
Thanks
I have done a E.I.C.R report on an installation with 16mm meter tails and 6mm Earth conductor. Whilst this is undersized and should be 10mm, using the adiabatic equations the 6mm is fine to carry the fault current. My question is this, the bonding is also 6mm and whilst I would recommend for this to be upgrade to 10mm, would you class this as unsatisfactory and fail an installation? As the bonding is present (albeit undersized) would you code this as C2 or C3?