Morning All,
Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC.
Earthing is TNS with main bonding requirements being 25mm2.
Using table 54.7 - CPC is half of line conductor so 35mm2.
Am I correct in thinking the 35mm2 conductor is adequate for both CPC and bonding requirements?
Cheers guys.