Morning All,

Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC.
Earthing is TNS with main bonding requirements being 25mm2.
Using table 54.7 - CPC is half of line conductor so 35mm2.

Am I correct in thinking the 35mm2 conductor is adequate for both CPC and bonding requirements?

Cheers guys.
 
Morning All,

Think I'm having a brain fart but I have a 70mm2 4 core SWA with a separate 35mm2 CPC.
Earthing is TNS with main bonding requirements being 25mm2.
Using table 54.7 - CPC is half of line conductor so 35mm2.

Am I correct in thinking the 35mm2 conductor is adequate for both CPC and bonding requirements?

Cheers guys.
Good morning,

That’s looking good, could probably manage smaller if you did Adiabatic but that’s on the safe side I guess.

So for 70mm² line if you select from the book it has to be (S / 2) so that’s your 35mm² main protective conductor. Then main bonding should be no less than half the main earth but need not exceed 25mm².

If I’ve missed anything let me know but all looks good to me.
 
The SWA of 4 core 70mm is 138mm² the equilalent in copper is 61mm², therefore the armour is big enough on its own.

Copper has a conductivity 8 times that of steel, so 138mm steel is equivalent to 17mm copper. So no, the armour is not sufficient to meet the requirements for bonding.

I think you may he confusing the calculation for suitable size of steel CPC with that for working out the 'copper equivalent' for the purposes of bonding.
 

Reply to Earthing and Bonding sizing. in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
953
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Thanks, I was hoping someone could confirm whether it was odd or not. I've done a fair bit of insulation testing but only on a small number of...
Replies
4
Views
286
  • Question
Why would the RCD fail … yes it can happen but then it may not. Without it you have no protection on the TT System
Replies
36
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top