Hi All,
All my work is commercial/industrial and I have a question on a domestic. Replaced a cracked socket at a friend's house for them and plugged in tester to do a quick Zs afterwards. 59ohms on a TNS = wrong.
Turned off the board and did a Ze which gave 58.5ohms although couldn’t connect the gas and water bonds. It’s a lead covered ancient cable. The earth bond on the cable which is loose has also had the Main Protective Bonding conductors connected directly to it, probably when the kitchen was installed a few years ago. I guess this was because the MET didn’t have enough ways. Obviously there are no certs for this work as my friend wastold they were only needed for a full rewire…….
Am I correct in thinking that the DNO is responsible for the Earthing Conductor from the sheath on a TNS to the MET?
They’ve gone away for a few days so it’s not a blue light job. I don’t fancy messing about with the clamp on the world’s most ancient cable. I’m proposing getting a proper size MET, reporting a high Ze to the DNO and getting them to sort it. They may make a charge I guess but that’s probably the best way out…..
All my work is commercial/industrial and I have a question on a domestic. Replaced a cracked socket at a friend's house for them and plugged in tester to do a quick Zs afterwards. 59ohms on a TNS = wrong.
Turned off the board and did a Ze which gave 58.5ohms although couldn’t connect the gas and water bonds. It’s a lead covered ancient cable. The earth bond on the cable which is loose has also had the Main Protective Bonding conductors connected directly to it, probably when the kitchen was installed a few years ago. I guess this was because the MET didn’t have enough ways. Obviously there are no certs for this work as my friend wastold they were only needed for a full rewire…….
Am I correct in thinking that the DNO is responsible for the Earthing Conductor from the sheath on a TNS to the MET?
They’ve gone away for a few days so it’s not a blue light job. I don’t fancy messing about with the clamp on the world’s most ancient cable. I’m proposing getting a proper size MET, reporting a high Ze to the DNO and getting them to sort it. They may make a charge I guess but that’s probably the best way out…..