SimpleSimon
Has anyone ever seen a supply neutral from the transformer that isn't earthed along the length of it?
Reason I ask is because finishing a TT install today, was getting about 100V between live and earth and about 70V between neutral and earth (237V between live and neutral) but my earth rod is fine and back at the start of my SWA in the board room. So I'm thinking broken neutral?
Any suggestions throw them at me because I didn't have any time to investigate, just powered it down and left thinking.
Reason I ask is because finishing a TT install today, was getting about 100V between live and earth and about 70V between neutral and earth (237V between live and neutral) but my earth rod is fine and back at the start of my SWA in the board room. So I'm thinking broken neutral?
Any suggestions throw them at me because I didn't have any time to investigate, just powered it down and left thinking.