S

SimpleSimon

Has anyone ever seen a supply neutral from the transformer that isn't earthed along the length of it?
Reason I ask is because finishing a TT install today, was getting about 100V between live and earth and about 70V between neutral and earth (237V between live and neutral) but my earth rod is fine and back at the start of my SWA in the board room. So I'm thinking broken neutral?
Any suggestions throw them at me because I didn't have any time to investigate, just powered it down and left thinking.
 
Just popped into my head frm somwhere doesnt the regs talk about voltages to earth in a tt not being greater than 50V:shocked3:
 
Last edited by a moderator:
hi, sounds like a L-E fault on the installation, IR test your cable and if origin is TT test the incoming RCD, if the origin is TNCS check Ze at origin and to true earth
 
Simon, what voltages are you getting at the board? Is this an O/H supply? Just asking to get some idea which way to turn.

By O/H do u mean old house?if so no it's a new supply but it's fed from a very old school hence why I didn't export the earth as I didn't entirely trust it.
Yes Jax sounds like an L/E fault, maybe a fault on the supply cable. I'll IR test it when I go back.
 
Right now that’s out of the way what are the voltages L>E N>E L>N.
E being your earth rod.


I’ll tell you now I’ve got my suspicions as to what it is, but I need the readings. And if it is what I think you’re going on a nature ramble!

MOST important is it a 3-phase local transformer? If it is this could affect other consumers.
 
Last edited by a moderator:
Do you know what happened Tony?!! Stupid plumber disconnected the conductor and buried it back in the ground without telling me. Stupid stupid stupid &@&£###
But I'm curious to know what your theory is/was?
 
I don't know Engineer. It wasn't even in his way. I popped by today, poked my head around the back to find a tap has magically appeared.
Once connected I got a Ze of 0.45 ohms and a Zs of 33 on my sockets. 
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Earthing at transformer
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
SimpleSimon,
Last reply from
SimpleSimon,
Replies
12
Views
1,585

Advert

Back
Top