SimpleSimon

Has anyone ever seen a supply neutral from the transformer that isn't earthed along the length of it?
Reason I ask is because finishing a TT install today, was getting about 100V between live and earth and about 70V between neutral and earth (237V between live and neutral) but my earth rod is fine and back at the start of my SWA in the board room. So I'm thinking broken neutral?
Any suggestions throw them at me because I didn't have any time to investigate, just powered it down and left thinking.
 
Simon, what voltages are you getting at the board? Is this an O/H supply? Just asking to get some idea which way to turn.

By O/H do u mean old house?if so no it's a new supply but it's fed from a very old school hence why I didn't export the earth as I didn't entirely trust it.
Yes Jax sounds like an L/E fault, maybe a fault on the supply cable. I'll IR test it when I go back.
 
Right now that’s out of the way what are the voltages L>E N>E L>N.
E being your earth rod.


I’ll tell you now I’ve got my suspicions as to what it is, but I need the readings. And if it is what I think you’re going on a nature ramble!

MOST important is it a 3-phase local transformer? If it is this could affect other consumers.
 
Last edited by a moderator:
Do you know what happened Tony?!! Stupid plumber disconnected the conductor and buried it back in the ground without telling me. Stupid stupid stupid &@&£###
But I'm curious to know what your theory is/was?
 
I don't know Engineer. It wasn't even in his way. I popped by today, poked my head around the back to find a tap has magically appeared.
Once connected I got a Ze of 0.45 ohms and a Zs of 33 on my sockets. 
 

Reply to Earthing at transformer in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
168
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
When I was at college doing the 2361 back in the 1980's I still recall to this day the instructor (Mr Wood) saying "Lads I do not want you to...
Replies
10
Views
684
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top