A sparky told me today that you dont have to earth metal back boxes if they are RCD protected???? Right or wrong??
Its what your sparky mate doesn't know, that scares us...........
Did you know about the fixed lug Electro![]()
I Agree but i have certaintly come across a lot who think they know it all.![]()
Come on fellas.
When the accessory is screwed back the earth connection to the box is provided through the fixing screw from the plate.
You will probably find the CSA of the screw is more then the 1.5 fly lead that would be connected.
Ive seen rusty and painted plate screws. I would rather just connect 4 inch of cable and be done with.
just taken a look on the NICEIC website and somebody asked the question ""
"Could you please tell me if it is neccasary to earth a metal back box if it has one fixed lug" The reply from the niceic was "Where an accessory has an earthing terminal incorporated, the protective conductor should be connected at the earthing terminal
Myself i would go with that.
.... may have the socket front off and if the cable is damaged at the entry to the box, then it may touch and liven the box. In that instance if the box wasn't fly leaded it could become live as the earth would be connected to the socket and the socket seperated from the box at the crucial moment.
Thats you on the naughty step then as you should not be working live.
Therefore if the socket front was removed and the above happened, then only you would be to blame if the inevitable happened.
Work safe guys![]()
Very true, but if you were trying to get a Zs at a light switch ................![]()