Earthing back to neighbours in terrace? | on ElectriciansForums

Discuss Earthing back to neighbours in terrace? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Nov 12, 2020
Messages
39
Reaction score
36
Location
Winchester, UK
Been asked to do some rewiring, and have said needs upgrade of consumer unit really
Main question is regarding earthing - Zs reads at 0.45 ohms (which suggests at TNS) But cannot see where earth cable goes to from old fuseboard.

There is no earth to fuse carrier or cable to fuse carrier in house.
Im guessing it goes to neighbour, and they actually have a looped supply.
Current cable is not even 10mm - and if earth is back to neighbours incoming supply - I guess I’d need to ask DNO about getting it switched to inside the clients house?

I can’t access neighbour to confirm all this conjecture - but have asked client to talk to them and get me a pic of their incoming supply
 
Been asked to do some rewiring, and have said needs upgrade of consumer unit really
Main question is regarding earthing - Zs reads at 0.45 ohms (which suggests at TNS) But cannot see where earth cable goes to from old fuseboard.

There is no earth to fuse carrier or cable to fuse carrier in house.
Im guessing it goes to neighbour, and they actually have a looped supply.
Current cable is not even 10mm - and if earth is back to neighbours incoming supply - I guess I’d need to ask DNO about getting it switched to inside the clients house?

I can’t access neighbour to confirm all this conjecture - but have asked client to talk to them and get me a pic of their incoming supply
probably a 6mm going to a water or gas pipe. You can always phone network power and ask them, you can also ask them if you can change it to a TNCS.
 
probably a 6mm going to a water or gas pipe. You can always phone network power and ask them, you can also ask them if you can change it to a TNCS.
Thanks - yes have asked if they can change to TNCS - 4-6 week lead time apparently

To sign off the work, I’d need to have visual site of adequate earthing and not just an ok reading - I don’t think Im being too ---- about this am I?
 
Thanks - yes have asked if they can change to TNCS - 4-6 week lead time apparently

To sign off the work, I’d need to have visual site of adequate earthing and not just an ok reading - I don’t think Im being too ---- about this am I?
No your right, because you've changed the DB and carried out remedial work you have to be able to confirm that the main earth and the bonding, if its necessary, is up to current regs.
 
To sign off the work, I’d need to have visual site of adequate earthing and not just an ok reading - I don’t think Im being too ---- about this am I?
I agree, you need to understand the earthing.
I guess there are no other clues, like an up front RCD or the old CU having a main switch RCD?

Also you said Zs, did you mean Ze, testing to the unknown cable while it was disconnected from CPC bar?
 
Thanks - yes have asked if they can change to TNCS - 4-6 week lead time apparently

To sign off the work, I’d need to have visual site of adequate earthing and not just an ok reading - I don’t think Im being too ---- about this am I?
No you’re correct in what you’re doing, although I’d expect the provider to be able to answer your question. If you make a case that it’s ‘unsafe’ I’m sure their response will be quicker.
 

Reply to Earthing back to neighbours in terrace? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top