H

hillbillie

I'm working in a warehouse, that was originally a factory. The electrics were put in in 1965 and were added to by successive owners over the next 20years and since then have been neglected.

Some of the boards have no earth so I thought I'd run some cable from the MET in the meter room to these boards. The problem is that the runs will be up to about 90 metres. Should I use the same standard that the OSG uses for bonding conductors (i.e. to ensure the circuit resistance is kept under 0.05 ohms) for these?

The earthing system for the premises is TN-C-S

Thanks.
 
Last edited by a moderator:
If you are talking about a CPC then you'll have to size it according to section 543, either from selection or calculation.

If the system is PME then 544.1.1 needs to be satisfied.

When you say the boards have no earth, are you sure trunkings/conduits aren't being used as a cpc?
 
The conduit is being used as the earth but this doesn't go everywhere. There are a couple of boards whose circuits don't go through the conduit.

the building has had bits bricked off and new bits added, it's a nightmare.
 
Last edited by a moderator:
The conduit is being used as the earth but this doesn't go everywhere. There are a couple of boards whose circuits don't go through the conduit.

the building has had bits bricked off and new bits added, it's a nightmare.

If that's the case then you need to recommend a periodic inspection.

The problem arises when you upgrade some of the earthing but miss other bits that you maybe weren't aware of, but as far as your boss/duty holder is concerned, "I thought everything was ok because hillbillie sorted it your honour".
 

Reply to Earthing cable from MET to other distribution boards in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for the advice! Much appreciated
Replies
6
Views
763
  • Question
I used one of those ‘safe digs’ web search, when I was considering an earth rod for my property, for a tub supply. It was a new build at the time...
Replies
10
Views
2K
  • Locked
  • Solved
Therein lies the problem. I see no merit in further circular debate, so will bow out of this discussion.
    • Like
2 3
Replies
55
Views
7K
nicebutdim
N
Just an FYI, there are contractors that do directional drilling. Some years ago at a previous job we looked into using one to link the network...
Replies
13
Views
7K
  • Question
One route could be to call the DNO and report the unsafe install, they may decide to pull the fuses on it...
Replies
11
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks