As I was being ushered out of the door after a brief pre-work visit I saw that the incoming neutral goes into a Henly block with an Earthing cable sticking out of it. The earthing cable was 10mm and it was just snipped off and had been left there. The CU was changed in 2012.

I have 2 questions, I have never seen a TNCS where the main earth is just attached to the neutral through a Henly block, would this have been ok as it is not in one of the recognised DNO cut outs as I have always seen before?

Also, the incoming line and neutral cables are seperate. The line goes through the cut out and the neutral into a Henly block. There is no sign of any other earthing cable , does this mean that it HAS to be a TT? I'm sure I'll be getting the work so will be investigating but was interested!
 
Some (older) service heads only had a fuse block for the line and the neutral is in a connector block like a Henly block.
If it is TNCS then this is where the earth would come be generated.
as per picture below.
[ElectriciansForums.net] Earthing Cable Sticking Out Of Neutral Henry Block?
 
Some (older) service heads only had a fuse block for the line and the neutral is in a connector block like a Henly block.
If it is TNCS then this is where the earth would come be generated.
as per picture below.
View attachment 32972
Many thanks Richard.
That's pretty much exactly what it looks like apart from the earthing cable has been cut off. I can't understand this? Why would it have been made into a TT? Thats assumung there is any main earthing.
 
Many thanks Richard.
That's pretty much exactly what it looks like apart from the earthing cable has been cut off. I can't understand this? Why would it have been made into a TT? Thats assumung there is any main earthing.
Sounds to me like it may have been TT in the first place and the 10.0 coming from the neutral service terminal block was added later to give a TN-C-S system often called PNB ( Protective Neutral Bonding ) when a TT system is altered. Is it possible when the CU was changed in 2012 that this earth was cut off and never reinstated, posing the question what is now earthing the installation the original TT system or nowt.
 
Sounds to me like it may have been TT in the first place and the 10.0 coming from the neutral service terminal block was added later to give a TN-C-S system often called PNB ( Protective Neutral Bonding ) when a TT system is altered. Is it possible when the CU was changed in 2012 that this earth was cut off and never reinstated, posing the question what is now earthing the installation the original TT system or nowt.

Don't see how it can be PNB, as PNB requires a single N-E link, and this cannot be guaranteed on a public supply Tx.
It will be PME, if you have TN-C-S in a domestic dwelling, unless they have a dedicated on site HV/LV Tx.
 
The only way to be 100% sure Is an enquirey to the DNO company if TNCS is available at the property or meter number as the photograph is inconclusive. It is not only a case of sticking an earthing conductor in the neural block. This may have been done incorrectly by some unqualified person or persons unknown for some unknown reason.
Quite often you will see an old PME label close by if it is TNCS.
 
PNB is exceptionally rare in a domestic situation and has nothing to do with converted TT systems. It has more to do with the earthing off a transformer supplying a single property in a remote location.
The photo could either be a 'homemade pme' connection or it could be dno supplied. Whenever I see this, if there is a dno pme label nearby then I accept this at face value, if there is not then I will enquire of the dno
 
The only way to be 100% sure Is an enquirey to the DNO company if TNCS is available at the property or meter number as the photograph is inconclusive. It is not only a case of sticking an earthing conductor in the neural block. This may have been done incorrectly by some unqualified person or persons unknown for some unknown reason.
Quite often you will see an old PME label close by if it is TNCS.

Bizarrely, that was exactly what I was told to do by a DNO at a domestic property recently.

The service head had a lead sheathed cable, with an earth clamped to the lead sheath. However there was also an earth rod with cable to the MET. I queried with the DNO if there was a problem with their earthing facility, as the supply looked a TN-S. Engineer visited the property and suggested I could convert it to PME. I said what you mean you convert the supply to TNC-S, he said ' what's that in English, do you mean PME?'. He said it would take weeks for one of their engineers to be booked to do it, he said I should just put new earth into service head neutral terminal and then into MET, reasoning that the supply cable in the road had probably been replaced with new cable, somewhere, which will have been changed to PME.
 
Bizarrely, that was exactly what I was told to do by a DNO at a domestic property recently.

The service head had a lead sheathed cable, with an earth clamped to the lead sheath. However there was also an earth rod with cable to the MET. I queried with the DNO if there was a problem with their earthing facility, as the supply looked a TN-S. Engineer visited the property and suggested I could convert it to PME. I said what you mean you convert the supply to TNC-S, he said ' what's that in English, do you mean PME?'. He said it would take weeks for one of their engineers to be booked to do it, he said I should just put new earth into service head neutral terminal and then into MET, reasoning that the supply cable in the road had probably been replaced with new cable, somewhere, which will have been changed to PME.

Well I hope you did not do that, it needs to be verified by the DNO , under no circumstance should you connect you main earth conductor into the N unless it is TNCS.
 

Reply to Earthing Cable Sticking Out Of Neutral Henry Block? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
  • Question
I thought it was just a head with a link, rather than a fuse. Just strange that it can be so easy to pull it out. Different if it was a lid which...
Replies
3
Views
697

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top