Hi all

I am looking for ideas for best practice for Earthing Conductors to a dual tariff CU. Should two 16mm Earthing Conductors from the MET be installed, one to each earthing busbar? Or one earthing conductor to one of the earthing busbars and a link of 16mm to the 2nd earthing busbar? Assume for now that 16mm in total will be an adequate size anyway (I'll be checking the regs/calc on that later tonight anyway). I have a job with a 20 year dual tariff single CU install that may need a few changes.

Thanks
 
If the original CU will need some changes being made, it would make far more sense to renew the CU, if as you say it's already 20+ years old.

If a CU has dual supplies (2 set's of tails to two DP isolators) to it then you'll need separate main earthing conductors from the MET to the separate earth bars within the dual enclosure...
 
yes i agree with engineer54, but can the earthing conductors be linked to create a better earth or would this pose a problem with RCD's? should any faults arise on either side of the CU?
 
If the original CU will need some changes being made, it would make far more sense to renew the CU, if as you say it's already 20+ years old.

If a CU has dual supplies (2 set's of tails to two DP isolators) to it then you'll need separate main earthing conductors from the MET to the separate earth bars within the dual enclosure...
effectively an `earth marshalling block`...which then splits off to the points it serves.....
in this case the 2 dis-boards
 

Reply to Earthing Conductor to dual tariff CUs in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
389
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
971
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top