Hi guys
I carried out an EICR a while back on a property with 3P 100A incomer and it only had a 16mm earth. I thought this was undersized, I made contact with the local DNO and had 2 replies, one said it was fine, the other said it should be 25mm.
Im trying to do the adiabatic equation for it, but its so long since I did one of these I want to ensure im getting it right.
S=(⎷(I2t))/k
so I being the possible fault current which was 2.4kA, 2400 squared is 5760000
t being the disconnection time, which for a BS88-2 at 2.4kA is 0.1
K being 143
im getting ⎷(5760000 x 0.1) = 758.95
758.95/143 = 5.3mm
5.3mm seems far too low, what have I missed?